Discuss Eicr bonding in the UK Electrical Forum area at ElectriciansForums.net

GarryJ

-
Reaction score
8
Evening all.

Just wondered what everyone's sequence was for inspecting/testing main bonding when carrying out EICRs?

I was at property recently and carried out a full 100% EICR. Everything was satisfactory and up to scratch - new 17th Ed split board / all circuits RCD protected there was a couple of code 3 items for no earth sleeving in pendants etc.

The property had both main water and gas services (TNC-S system) There was an isca block at the origin with 16mm earth going into consumer unit and 2 x 10mm earth cables disappearing under floor.
The main water stop cock according to the tennant was under the utility room floor and the gas box was on the side of the house but no bonding visible inside external box. (Main gas pipe also comes into property under floor.)

I classed these as a Code 2 and requiring further investigation. On front page of certificate I stated this in the agreed limitations stating it was unaccessible.

However since I was last there British gas has been in to provide gas safe certificate and can not do this as they also say they can not confirm main gas is bonded?

Thanks in advance for any help
 
you couls always run a wander lead from MET to gas pipe close to point of entry, same with water. then, if continuity has been established, a code C3 for being inaccessible.
 
Evening all.

Just wondered what everyone's sequence was for inspecting/testing main bonding when carrying out EICRs?

I was at property recently and carried out a full 100% EICR. Everything was satisfactory and up to scratch - new 17th Ed split board / all circuits RCD protected there was a couple of code 3 items for no earth sleeving in pendants etc.

The property had both main water and gas services (TNC-S system) There was an isca block at the origin with 16mm earth going into consumer unit and 2 x 10mm earth cables disappearing under floor.
The main water stop cock according to the tennant was under the utility room floor and the gas box was on the side of the house but no bonding visible inside external box. (Main gas pipe also comes into property under floor.)

I classed these as a Code 2 and requiring further investigation. On front page of certificate I stated this in the agreed limitations stating it was unaccessible.

However since I was last there British gas has been in to provide gas safe certificate and can not do this as they also say they can not confirm main gas is bonded?

Thanks in advance for any help

Yes can be a tricky one really, best you can do in that situation is use a wander lead and measure resisstance from met to incoming service points and see what you got

if i had readings of under .05 ohms and i could see the 10mm cables going out from the board i would probably code 3 it with a recommendation of further investigation

if the readings were high i would probably code 2
 
Yes can be a tricky one really, best you can do in that situation is use a wander lead and measure resisstance from met to incoming service points and see what you got

if i had readings of under .05 ohms and i could see the 10mm cables going out from the board i would probably code 3 it with a recommendation of further investigation

if the readings were high i would probably code 2

Why 0.05 ohms?
 
youse gotta be quick to beat this old scouser. how d'ya think we get away with all them stolen cars?
 
Not set in stone, just a loose figure really bandied about in GN3, if it was too much over that i would think its not bonded directly with 10mm, unless it was a fair old distance

Whereabouts in GN3 is it 'bandied about'?

There is a figure of 0.05 given as a suggested maximum value for the resistance between the cable termination at the bs951 clamp and the pipe itself.
 
Whereabouts in GN3 is it 'bandied about'?

There is a figure of 0.05 given as a suggested maximum value for the resistance between the cable termination at the bs951 clamp and the pipe itself.

good post. that 0.05 figure is misunderstood by so many sparks as being a max. value for the resistance of a main bonding conductor.
 

Reply to Eicr bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Greetings, I am homeowner and looking to confirm if I will need earth boding to water pipes. There is already earth boding near Gas meter and the...
Replies
23
Views
601
Did a eicr on a upstairs flat, there is 1 main bonding cable from the consumer unit, the gas pipe comes from the gas meter outside and up the wall...
Replies
21
Views
3K
I am due to carry out an electrical job in a third floor flat. Incoming supply is TN-S. Cannot locate a main earthing conductor inside the CU on...
Replies
4
Views
2K
Hi guys I’ve seen people state in forums that it is permissible to bond a gas pipe as a continuation of the bonding of the rising water mains. Can...
Replies
3
Views
5K
Just had a boiler put in on a grant scheme. Water main earth bonding was connected in with the existing gas bonding's pipe clamp on the outlet...
Replies
20
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock