Dave_

-
Reaction score
24
Hi Gents

Just wanted opinions on the above

I know there are various factors that could sway opinion...

Customers that have a large house with downlights throughout are not too pleased when you give them a four figure quote to rip out the lot......

Cheers

Dave
 
You wasn't the kind chap who told one of my customers all the downlighters i had fitted in her bungalow bathroom were 'illegal' and were about to catch fire at any moment and had to be replaced with fire rated ones immediately?

thanks for that!
 
Hi Gents

Just wanted opinions on the above

I know there are various factors that could sway opinion...

Customers that have a large house with downlights throughout are not too pleased when you give them a four figure quote to rip out the lot......

Cheers

Dave

If the ceiling is a fire barrier then it will fall under section 527 which requires that the fire barrier not be compromised by the electrical installation.
I would give a C3 code as it is not presenting an electrical danger but is a recommendation of an improvement for safety.
 
Hi Gents

Just wanted opinions on the above

I know there are various factors that could sway opinion...

Customers that have a large house with downlights throughout are not too pleased when you give them a four figure quote to rip out the lot......

Cheers

Dave

If the ceiling is a fire barrier then it will fall under section 527 which requires that the fire barrier not be compromised by the electrical installation.
I would give a C3 code as it is not presenting an electrical danger but is a recommendation of an improvement for safety.

Spot on. Exactly my view too.
 
and do we also seal up the stairwell to stop fire from spreading upstairs? bunk beds in the kitchen.
 
If the ceiling is a fire barrier then it will fall under section 527 which requires that the fire barrier not be compromised by the electrical installation.
I would give a C3 code as it is not presenting an electrical danger but is a recommendation of an improvement for safety.

To a separate property?
 
and do we also seal up the stairwell to stop fire from spreading upstairs? bunk beds in the kitchen.
Tel your a genius, and the best guy on here without a doubt. I had exactly the same comment from a BCO the other day. Fire rated ruddy nonsense most of this, when you have the biggest Flu you could ever imagine in the shape of the stairway.
If someone has told a customer they have to have them all ripped out he should put on a mask and change his name to Turpin, and not Betty.
 
in an average single family house, the only requirement for fire rated downlights is in the ceiling of an integral garage.
 
To a separate property?

Any fire barrier, so it could be the barrier to an upstairs flat, or the ceiling of a built in garage, or the ceiling below a loft room where BC have required that fire door etc be fitted to separate that loft room, or even if the downright is installed in the pink fire line plasterboard boxing in an RSJ.
Plus of course the normal ceiling where it give 30minute protection to the void containing the floor joists.
 
Any fire barrier, so it could be the barrier to an upstairs flat, or the ceiling of a built in garage, or the ceiling below a loft room where BC have required that fire door etc be fitted to separate that loft room, or even if the downright is installed in the pink fire line plasterboard boxing in an RSJ.
Plus of course the normal ceiling where it give 30minute protection to the void containing the floor joists.

How many people fit downlights in their garages?
 
Any fire barrier, so it could be the barrier to an upstairs flat, or the ceiling of a built in garage, or the ceiling below a loft room where BC have required that fire door etc be fitted to separate that loft room, or even if the downright is installed in the pink fire line plasterboard boxing in an RSJ.
Plus of course the normal ceiling where it give 30minute protection to the void containing the floor joists.
That's just downlight daft.
 
aren't RSJs non-combustible steel since wooden ones are now outlawed under amd.3?
 
Hi Gents

Just wanted opinions on the above

I know there are various factors that could sway opinion...

Customers that have a large house with downlights throughout are not too pleased when you give them a four figure quote to rip out the lot......

Cheers

Dave
Whats the horse called?
 
I now understand why the buildings in 911 were weakened by fire to the point of collapse .

Full of plastic consumer units and non fire rated down lights . :ninja:

If they had them in 911 they must have had 'em in 1666.
A few weakened in then too......did clean things up after the 'great plague', though.
 
It is not the down-lights going up in flames that is the problem. The problem is the 75mm holes, you have cut in a half-hour rated plasterboard ceiling, allowing the fire to spread.


On a side note, never seen a fire rated ceiling speaker, have seen many of those installed lately, must be at least a 200mm hole in the plasterboard

are the audio/visual guys fitting speaker sized fire hoods nowadays?
 
Last edited:
On a side note, never seen a fire rated ceiling speaker, have seen many of those installed lately, must be at least a 200mm hole in the plasterboard

are the audio/visual guys fitting speaker sized fire hoods nowadays?

Yes they are. Daz
 
My bedroom door, when left open, provides an even bigger break in the fire resistant wall it's installed in.

However I don't understand anyone fitting non fire rated downlight nowadays, when even the most expensive ones are a few pounds. I wouldn't fit the open can tuppeny happeny tack sold by DIY stores. You're right about the speakers and what about ceiling extractor fans, you can get intumescent collars for them :)

OP mentioned a large dwelling house; Approved document B defines such as a residential accommodation occupied.... b) by not more than 6 people, living together as a single household. Not suggesting he should rip out existing luminaires, just as a discussion point for the original installation.
 
Hoods are available for speakers and should be fitted if required, just the same as down lighters. Daz
 

Reply to EICR Classification Code for downlights that are not fire rated in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi there fire rated down lights in a dropped false ceiling with no insulation and 2.5 watt LED lamps in cladding in kitchen with room space above...
Replies
10
Views
1K
Another accidental landlord, quite possibly another dodgy EICR? I instructed an electrician (Essex area) to perform an EICR at the house I rent...
Replies
12
Views
2K
Hey all, Could do with some help. I had a company recommended to me who quoted me to do an EICR on my rental property. (£265). I thought this...
Replies
5
Views
2K
Hi All Am continuously getting failed EICR'S sent over to quote on remedials for non fire rated downlights. These are lights in question. I see...
Replies
17
Views
5K
Good evening, I am just wondering whether or not non fire rated downlights should be a coded issue (c3 as many electricians have told me) or...
Replies
14
Views
20K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock