Discuss EICR Code in the UK Electrical Forum area at ElectriciansForums.net

H

highspark

Would a C3 be adequate for a main protective bonding conductor connection to water not readily accessible?

Connection is present (along with tag) but is under floor boards. Took me ages to trace it back.

Also I can not verify the location of the gas bonding connection. What code?
 
Why a C3 for the bonding being present but not accessible?
Have you tested the gas pipe to find if it's a extraneous conductive part?
 
Yes gas is extraneous and is connected but I can't locate the connection.

I'm presuming by your response NV would be more suitable for item number 3.7: condition and accessibility of main protective bonding conductors and connections.
 
I would be happy to code it C3. There is a specific section on the EICR form that requires an entry for the condition and accessibility of bonding conductor connections.
This can be backed up by 543.3.2 Every connection and joint shall be accessible for inspection testing and maintenance.

 
Yes gas is extraneous and is connected but I can't locate the connection.


I'm presuming by your response NV would be more suitable for item number 3.7: condition and accessibility of main protective bonding conductors and connections.
How do you know it's bonded if you can't verify the connection, continuity or CSA of the cable?
I would be happy to code it C3. There is a specific section on the EICR form that requires an entry for the condition and accessibility of bonding conductor connections.
This can be backed up by 543.3.2 Every connection and joint shall be accessible for inspection testing and maintenance.

The OP has said they have verified the connection so must be accessible?
 

Reply to EICR Code in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
825
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
4K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Can someone sanity check my thinking please.... An 80 amp PME service head, tails to meter, 25 sq mm tails into an enclosed fused isolator with...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock