Discuss EICR Flood in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
11
Hi Guys

on a job that was affected by recent floods carrying out an EICR

My question is that although the downstairs and kitchen rings are testing up ok I have concern because the cables that were run under floors were sat in water for over 4 weeks. I can't find all JB's but there must be more and I also think that having sat in water for this long it could cause problems in the long run with life of cable etc? I am recommending that based on the information that the downstairs rings should be rewired. Am I being unreasonable?

Cheers
 
If there were no joint boxes under the downstairs flooring then I would say don't really worry about it if everything is testing out fine, just recommend changing all socket outlets etc and checking the cable ends for corrosion etc and go from there. At the end of the day, cables can be ran outside (where they get wet) and so it's no different IMO.
If however you say there are joint boxes under the floor then it's not ideal as they will have been filled with water. TBH it's hard to say what to do without seeing it, only you can really make the call!
 
Hi Guys

on a job that was affected by recent floods carrying out an EICR

My question is that although the downstairs and kitchen rings are testing up ok I have concern because the cables that were run under floors were sat in water for over 4 weeks. I can't find all JB's but there must be more and I also think that having sat in water for this long it could cause problems in the long run with life of cable etc? I am recommending that based on the information that the downstairs rings should be rewired. Am I being unreasonable?

Cheers

what do your results tell you along with the condition of the visually inspected jb's.

no one else has seen it so cant really comment
 
Well rewire it is then, if it were me. I wouldn't be happy signing a certificate saying its fine when I know there's other JB's under the floor I haven't seen!
If it's in a flood prone area then maybe run the cables down the wall from upstairs and mount the sockets slightly higher up the wall. That way if there's another flood they won't need another added expense of a rewire again!
 
First of all, its not a certificate, its a report. And that is what you are there to do, to report on the items.

On the front of a EICR it states : ''It should be noted that cables concealed within trunking and conduits, under floors, in roof spaces and generally within the fabric of the building or underground, have NOT been inspected unless specifically agreed between the client and the inspector prior to the inspection''

Therefore if you weren't asked to do it, just make a comment saying you haven't done it e.g operational limitations.

You and you alone can make the decision If you think there are some latent defects existing within the installation, state it.You can only inspect and test to as far as is reasonably practicable.
 

Reply to EICR Flood in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I am never quite sure if I am doing too little or too much when someone has a flood and I am called in. The most recent example is a chap has had...
Replies
4
Views
823
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
705
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
789
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
809
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock