Search for tools and product advice,

Discuss Eicr insulation resistance testing in the UK Electrical Forum area at ElectriciansForums.net

GarryJ

-
Reaction score
8
Hi All.

I am currently carrying out an EICR in a local hotel. I was wondering how each of you carry out insulation resistance testing during a periodic inspection?
For lighting etc I have used joining live-neutral together and testing to earth due to the unknown possibility of electronics and lamps etc throughout the circuits.
It is an old Dorman Smith DB 3pH and I turned off the main switch of the DB which powered the full insulation down then disconnected the main earth from the isca block which was coming from the TNC-S cable head. I was getting a dead short between this isca block to the neutral bar of the DB after this earth was disconnected. I am aware back at the transformer earth and neutral are connected but once the main earth is removed I thought it would have been clear?
Would parallel paths cause a dead short? I.e the main bonding to water and gas?


Thanks in advance for any help with this

Garry
 
Yes I have disconnected main earth band going from cable head to isca block where DB and bonding are connected into and I am getting dead short between isca block and neutral bar in DB. Am I missing something
 
Why? and what do you do if you get a out of spec result when testing at the tails?

How would you find a fault between L or (normally) N and say some pipe work in the building if you start disconnection earths.
As for testing at the isolated side of your iso and you get poor results (the norm) you would sub divide the install but still leave all your earthing connected.
 
Sound like you have left the main neutral connected, you need to remove the link or disconnect the neutral conductor from the bar.

All earths are left in place when IR testing unless you are testing an individual circuit.
 
Sound like you have left the main neutral connected, you need to remove the link or disconnect the neutral conductor from the bar.

All earths are left in place when IR testing unless you are testing an individual circuit.

Your CPC will still need to be connected to MET when doing a single circuit or how else would you find the fault i said earlier.
 
What do you mean re a dead short are we talking 0.00 Meg Ohms or 0.00 Ohms or could it possibly be K Ohms ?

If you are testing the entire installation at the tails and if only one circuit is low it will bring your reading down!

You will have to start testing each circuit on its own until you find the circuit / circuits !
 
Cracked it!! I have forgot to remove the link before testing. For all the individual circuits I have tested I have removed the neutral and CPC from each of the bars and then carried out IR but just when testing the mains I have forgot to remove the link. If no link is present removing the main neutral and testing from the MET to the neutral bar with all circuits neutrals is correct?

Thanks
 
So it was basically a 3 pole main switch with solid neutral which you had left connected whilst carrying out your insulation tests. Guess you have not done much testing on 3 phase systems.
 

Reply to Eicr insulation resistance testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
650
No waffling, going to get straight to the point. Main water on the exterior of the building in plastic. Changes to copper inside the building...
Replies
24
Views
947
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K
Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
773

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock