hi all,
Ok let’s get straight to the question.
Is the below a code 2 defect on a EICR??
A 16amp bs61009 supplying a single 1.5mm FP200 cable with a run of approximately 8 meters, which is feeding a IP rated single socket for a grease trap unit. The socket is low level behind the grease trap and it’s sole use is to supply the grease trap ( no extension leads or anything as in a commercial kitchen ).
I’m 95% sure 1.5mm fp is rated at 16.5 amps when enclosed and 19 amp when in free air?
The run is on tray with a 1.5m drop of 20mm PVC conduit down to the socket.
Ok let’s get straight to the question.
Is the below a code 2 defect on a EICR??
A 16amp bs61009 supplying a single 1.5mm FP200 cable with a run of approximately 8 meters, which is feeding a IP rated single socket for a grease trap unit. The socket is low level behind the grease trap and it’s sole use is to supply the grease trap ( no extension leads or anything as in a commercial kitchen ).