When we have recently undertaken a EICR on a large hotel,we have found that the 13amp sockets within the bedrooms are not protected by an rcd,and obviously can be used for any use by ordinary persons.Should we advise to protect them by rcd's to comply with current regs,although the rest of the building could considered to be managed,the bedrooms are not.Just fitting labels to them stating for hotel equipment only seems implausible,any thoughts.
 
It's a grey area, if cables are installed where RCD protection is not required, then you have to assess risk to public. Especially on upper ground floors where current using equipment will not be used outdoors. We usually recommend it for additional protection.
 
It's a grey area, if cables are installed where RCD protection is not required, then you have to assess risk to public. Especially on upper ground floors where current using equipment will not be used outdoors. We usually recommend it for additional protection.

Well said that man perfect answer to the question,
 
What edition of the regs was the installation installed to. If it complies to the edition to which it was installed then you can only give it a code 3.
 
It's a grey area, if cables are installed where RCD protection is not required, then you have to assess risk to public. Especially on upper ground floors where current using equipment will not be used outdoors. We usually recommend it for additional protection.

Do you think that a guest in a ground floor hotel room will be using an electric lawnmower or hedge trimmer then? :grin:
 
It's a grey area, if cables are installed where RCD protection is not required, then you have to assess risk to public. Especially on upper ground floors where current using equipment will not be used outdoors. We usually recommend it for additional protection.

Do you think that a guest in a ground floor hotel room will be using an electric lawnmower or hedge trimmer then? :grin:

Ha ha yes very good point maybe it's a working holiday
 
So are sockets only allowed to be used by guests? The hotels we inspect have patio doors on all ground floor rooms where I have witnessed maintenance staff plugging extension leads into to room sockets when required.
No need to be sarcastic.
 
What does the version of the regs to which they were installed say about ground floor sockets that can be used for portable equipment outdoors.
 
So if a car was built before airbags were introduced then the MOT station can fail it yes ?

Surely it would be good advice to advise the customer of how much safer their car would be with the new added safety features.
If they where conscientious they may deem it worthwhile investing

Not doesn't have to be done but what harm can it be to advise clients an upgrade is well worth considering
 
Surely it would be good advice to advise the customer of how much safer their car would be with the new added safety features.
If they where conscientious they may deem it worthwhile investing

Not doesn't have to be done but what harm can it be to advise clients an upgrade is well worth considering

Correct that's why you C3 it but you cannot force them to do it ie C1 or C2 it so why am I reading posts like this where people are doing this
 
On a personal note I have been advised by some clients they will only ever consider remedial work on Cat 1 and 2 and leave all Cat 3 altogether.

If this was the case here then RCD to sockets will never get upgraded.
I'm just saying better be safe than sorry
 
Not overly relevant, they can only compare to standards it was built to. We have to consider current regs as well as those it was installed to.
Dave sorry to say it is relevent because you can have an installation with a 3036 CU that was installed to the regs at that time and if it tests out ok then it passes . i have said this before here when doing an EICR you can advise via C3 to get RCD protection but you should not C1 or C2 because if you do it can come back to bite you like the landlord who was told he had to have RCD protection for a rental property and got a full refund from the company who put this in writing to him after he paid them to change the CU
 
So are sockets only allowed to be used by guests? The hotels we inspect have patio doors on all ground floor rooms where I have witnessed maintenance staff plugging extension leads into to room sockets when required.
No need to be sarcastic.

Only a bit of amusement mate, no offence intended. (Hence the smiley.)
 

Reply to EICR on large hotel in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Did a couple of inspections on 2 x 2 bed ground floor flood damaged flats today, only 4 circuits in each, bizarrely one socket circuit and 2...
Replies
6
Views
2K
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
6K
I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I...
Replies
29
Views
4K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
4K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
178

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock