Discuss Eicr question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

R

RISElectrical

Block of flats, 3 phase incomer split to feed 3 flats, PME coming in with a 16mm earth. This then feeds a 60a switched fuse that feed the flat. The cpc leaves the switch fuse as 6mm and then clamps to the armouring of a 10mm 2 core swa that goes up 2 floors to the flat db. At the flat db 4 strands of the armouring are then used for the cpc.

I have 2 questions that I'm unsure of. 1. What size would you record on the eicr for the earthing and 2. What would you code the 4 strands of armouring being used at the db? C2?

Any thoughts?

Thanks
 
my opinion

C2 and C2 to both

is the arnouring being used as the main bonding contctor to the incoming services within the flat ?
 

Reply to Eicr question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
810
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock