If a shower was fitted 15 years back and had no rcd what cat would it be on a eicr
Discuss Eicr question in the UK Electrical Forum area at ElectriciansForums.net
Not according to the ESC Electrical Safety Council
From 4. Periodic inspection of existing domestic and similar installations : Electrical Safety CouncilQ4.4
What Classification Code should be given if it is found that there is no supplementary bonding in a bathroom having extraneous- or exposed-conductive-parts, and the conditions given in Regulation 701.415.2 for its omission are not met?
Classification Code C2. Where the presence of supplementary bonding cannot be confirmed by inspection, it may be verified by a continuity test (< 0.05 ?)
None. You are not testing to the 17th regs.
If the bonding is fine then if it is is someone own home a C3 if it is a rented accommodation C2
Doesn't that say its code 3 if it has bonding?Its code 3 regardless of bathroom bonding or not.
From the ESC EICR guidlines giving examples of C3's ;
"Absence of RCD protection in a location containing a bath or shower where satisfactory suplementary bonding is present "
Its all there , clear as crystal but nobody could be arsed looking the facts up properly.
Apart from me ;-)
Where is the link to this please Biff, I can't find it on their site. Or are you looking at an old leaflet?
Doesn't that say its code 3 if it has bonding?
But that says the opposite of what you are saying
It says exactly what I have said that it does depend on whether the Supp bonding is present
What did we do before these wonder rcd's came about!
Rcds are nice little items for giving that little bit of extra back up (TT excepted), however, well constructed and maintained electrical systems are the best target
it int a 2....you base an EICR on what was compliant AT THE TIME OF INSTALL....That's what I've all ways thought but a sparky has gone to do some wrk there and said it should be cat 2
Lets be clear, on an EICR.
Lack of RCD protection to a circuit in the bathroom attracts a C3 providing proper supplementary bonding is in place
Lack of RCD protection to a circuit in the bathroom attracts a C2 if no supplementary bonding is in place
Cables buried above 50mm in a Wall attract C3
I always check supplementary bonding is proper and covers all points including radiators etc. if necessary - Readings should be 0.05 or below.
So a bathroom wired to the 16th could easily attract 4 C3's