Its code 3 regardless of bathroom bonding or not.
From the ESC EICR guidlines giving examples of C3's ;

"Absence of RCD protection in a location containing a bath or shower where satisfactory suplementary bonding is present "

Its all there , clear as crystal but nobody could be arsed looking the facts up properly.
Apart from me ;-)
Doesn't that say its code 3 if it has bonding?
 
On my reports I will only put things that can be justified by the industry advice or the regs. I will be able to say where an opinion came from. I think this is important myself.


You Said
Its code 3 regardless of bathroom bonding or not.
From the ESC EICR guidlines giving examples of C3's ;


But the document you referred to said

Absence of RCD protection for circuits of a
location containing a bath or shower where
satisfactory supplementary bonding is present


Good greif man if you are gonna be arsed to look it up - quote it right too!
 
I would be wound up if someone gave a c2 to my non rcd'd shower. As I say it was compliant to install up until 4 years ago, it's not 'potentially dangerous'. That's just drumming for work imo Supplementary bonding is an adequate.
What did we do before these wonder rcd's came about!
 
Yes but do you rent your house out?
If you did the Landlord and Tenant Act plus the insurance for letting might make you feel it is better to have the place kept to the latest editions of the wiring regs. Professional landlords in my experience want to be watertight when it comes to insurance
 
Rcds are nice little items for giving that little bit of extra back up (TT excepted), however, well constructed and maintained electrical systems are the best target

I think the (TT Excepted) gives the game away here.
They provide additional protection against electric shocks - over and above what even the best designed electrical system can achieve without them.
They are not an excuse for poor design, however if main bonding is in place, and the system is properly maintained and constructed, it is well accepted that supplementary bonding may be omitted.
That is the point of having the test of whether RCD is a required in the latest regs page 199, 701.415.2

If you are auguring that the we should return to the 15th editions or something - actually that's not what you are suggesting is it?
 
I agree with martinxxxx here. The best practice guide recommends that where there is no rcd protection and no supplementary bonding then it definitely is a C2.
But remember to carry out a continuity test to check whether there is supplementary bonding or not.

Yes the test is carried out to check compliance with regs at time of install and anything which is not to current regs is a C3. However don't forget that the requirement for supplementary bonding in the bathroom was still a requirement in the previous editions of Bs 7671
 
Last edited:
Lets be clear, on an EICR.

Lack of RCD protection to a circuit in the bathroom attracts a C3 providing proper supplementary bonding is in place
Lack of RCD protection to a circuit in the bathroom attracts a C2 if no supplementary bonding is in place
Cables buried above 50mm in a Wall attract C3

I always check supplementary bonding is proper and covers all points including radiators etc. if necessary - Readings should be 0.05 or below.

So a bathroom wired to the 16th could easily attract 4 C3's

A C2 for a shower is over zealous if supplementary bonding is in place.
I have worked testing for a social landlord, they would never ask for RCDS on all showers regardless, the cost could be huge for virtually no gain in safety. They will insist on enclosed bathroom fittings, even if outside of zones.
 

Reply to Eicr question in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock