Hi guys

I am doing an EICR for a friend - older build all current works pre-17th edition

have failed the bathroom - no supplementary bonding on pipe work and there is not RCD present

i am going to give a C2 for supplementary bonding and C3 recommending to install RCD

By doing this I am only upgrading to the 16th edition regs.

Would this be satisfactory or should it be upgraded to the 17th edition.

Normally I would recommend upgrading to 17th edition but I'm trying to keep the cost down for them.
 
no. give it a C2 for " no supplementary bonding and no RCD". that is all you need to do. in comments, just state that the fitting of a RCD may negate the need for supp. bonding.
 
Does it need supplementary bonding ?
Have you tested to see if it needs it ?, bear in mind supplementary bonding may be made outside the room.
 
Last edited:
no. give it a C2 for " no supplementary bonding and no RCD". that is all you need to do. in comments, just state that the fitting of a RCD may negate the need for supp. bonding.

Agree with what you've written and normally this is what I would do

as we're trying to keep costs down was going to install the supplementary bonding myself and log the work as C3 recommending installation of RCD

my worry is that this will be restoring the installation to 16th edition regs and although it was installed ages ago not sure I'll be able to leave it like that
 
As already said, supp bonding may not be needed depending on the test results achieved. If this is the case you'd only be dealing with the lack of an RCD for additional protection which would be a C3 as you have stated.
 
Last edited:

Reply to EICR supplementary bonding query in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Hi everyone Sorry if it's a repeated question tho. Agents followed me a failed visual EICR which has C2 for lack of RCD on cooker circuit and...
Replies
11
Views
1K
Good Afternoon All Currently doing an EICR on common parts of a big site with multiple blocks. All blocks have outside garden spike lighting in...
Replies
11
Views
534
Curious about supplementary bonding, I have these two 4mm Cables loose and not connected to anything in my parents house. I presume they are for...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock