Discuss Elec towel rail in downstairs washroom. in the The Welcome Forum area at ElectriciansForums.net

Reaction score
0
Heyo, having a new downstairs washroom, sink, basin, boiler and elec towel rail. The electrician tells me that under the latest IEE 17th ed regs its OK to have the switch for the towel rail inside the washroom in the zone 2 area, as there's no steam from a bath or shower - is this correct ? I always thought it had to be outside of the room. The washroom will be on its own isolator with separate mini consumer unit with rcd and otherwise complies with the 17th, having an isolator above the door on the outside etc. Thanks guys.
 
as long as there is no bath or shower, it's not a "special location" under 701, so your electrician is correct.
 
Hi , thanks Guys - just everywhere I've been with these elec towel rails the switch has been outside the room - but they all had a bath or shower in there. And the council building inspector is going to return so just wanted to make sure all was perfect.
 

Reply to Elec towel rail in downstairs washroom. in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

One of the oddest jobs I've ever had today. Called by a plumber I know who had attended after a leak through the kitchen ceiling from bathroom...
Replies
24
Views
6K
We're having an electric towel rail installed in bathroom, outside any zones It's just above the stairs with a clear wiring run to under the...
Replies
27
Views
12K
Hi. I am fitting an electric towel rail in Zone 2 - it is IP55 rated so fine there. The flex coming out of it I have a few options - There is...
Replies
9
Views
8K
Hi all, It seems to be normal practice to mount electric timers outside the bathroom, but so long as its outside zone 2 a towel rail timer can be...
Replies
14
Views
17K
Landlord has had an EICR done on the property as is required under the new PRS legislation, got a copy of the report and I'm not overly impressed...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock