Discuss Electric Towel rail in Bathroom connection question in the UK Electrical Forum area at ElectriciansForums.net

Robsi1

DIY
Reaction score
0
Hi.

I am fitting an electric towel rail in Zone 2 - it is IP55 rated so fine there.
The flex coming out of it I have a few options - There is currently a cable going from the consumer unit into the bathroom making its own circuit (used to be for boiler but not used now)
I have a couple of options -

1) Connect the flex directly up to a cable that goes into the consumer unit - I would connect the flex cable from the radiator to the mains cable under the floor with one of these - IP68 Waterproof 3 Pole Plug and Socket Cable Connector 32A 450Vac - https://sinolec.co.uk/en/rewirable-socket-plugs/1211474--ip68-waterproof-3-pole-plug-and-socket-cable-connector-32a-450vac.html?utm_source=GoogleShopping&utm_medium=cpc&utm_campaign=ExportPrestashop&gclid=CjwKCAjwuITNBRBFEiwA9N9YEP9bPrVuya3vwK2DIKnnw0-1q6WzjR2X46r3DE7HDyLt62qeBv9GDxoCWvYQAvD_BwE

2) Connect the flex to an (unfused) Connection unit on the wall next to the radiator and then connect the other end to this cable that goes directly to the consumer unit (no switch/fuse between the 2 - other than the fuse in the fuse board)

3) (my least prefered option) - Connect the radiator to a (unfused) Connection unit next to the radiator then run a cable to a fused connection unit outside of bathroom and then onto the consumer unit


Is option 1 or 2 possible i.e. a connection without a fused switch on the wall somewhere?
 
Any electrical work within the zones of a bathroom is legally notifiable to building control. Appropriate testing and certification should also be carried out for this alteration.
Any accessories installed in zone 2 should be at least IP44.
Any cable joints/connections should be accessible for inspection and maintenance unless they are joined in a maintenance free fashion as described in the wiring regulations.
The manufacturer's instructions for the radiator may require a fuse to protect the cable supplying the appliance so the unfused idea may not be an option.
 
Does the element have a timer built in to it? If not, you may want to consider adding a timer as you likely won't want the towel rail running 24/7. Something like this located in a suitable position would provide local isolation, a fuse and timer:

https://www.NoLinkingToThis/p/green...ay-fused-digital-timer-spur-switch-230v/7643g

You will need access to the connections to the heating element to replace it should it ever fail so a suitable connection unit on the wall would make sense.

As others have said:

This is notifiable work. There are lots of things to consider when doing electrical work in a bathroom so you really need to know what you are doing and have the appropriate test gear. It does sound like you might be best off getting an electrician in for this job.
 
Smallest breaker/fuse/mcb/rcbo you’ll get will be 6a ish and I’d expect the radiator will need fusing down further so you’ll need a sfcu....as others have said legally notifiable...


Wrong
https://www.NoLinkingToThis/p/schne...MIuIy1veeI5gIVhLHtCh0oOABEEAQYAiABEgJYKfD_BwE

https://www.NoLinkingToThis/p/schne...MIuIy1veeI5gIVhLHtCh0oOABEEAQYAiABEgJYKfD_BwE
[automerge]1574805471[/automerge]
@Baddegg what do you dislike about the above post as it is factual unlike your previous post!!
 
Last edited:
Wrong
https://www.NoLinkingToThis/p/schne...MIuIy1veeI5gIVhLHtCh0oOABEEAQYAiABEgJYKfD_BwE

https://www.NoLinkingToThis/p/schne...MIuIy1veeI5gIVhLHtCh0oOABEEAQYAiABEgJYKfD_BwE
I can only apologise profusely for my lack of knowledge on this matter @bigspark17....please forgive me I will now go and self flagellate myself and won’t let this abhorrent slip happen again....if that fella happens to have a schieder consumer I don’t think I’ll ever get over this ?
I know I was wrong but showing me twice is just rubbing salt in the wound mate...
 
Last edited:

Reply to Electric Towel rail in Bathroom connection question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

i have just started my course as a trainee electrician...some advice on the following will be appreciated: I have a spare 16 and 32A MCB (RCD...
Replies
5
Views
207
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
659
I have had my kitchen rewired ready for a new kitchen. I was originally going to have a gas cooker so a 3 pin 13a socket was left on the end of...
Replies
2
Views
377
Hi, I'm looking for some advice please. I'm not an electrician but have employed a registered qualified one to do some work for me and want to...
Replies
5
Views
1K
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock