Electric boiler as in smallish rectangular box that runs a heating system, or electric boiler as in hot water storage cylinder?
Discuss Electric boiler service in the Central Heating Systems area at ElectriciansForums.net
Interesting that there is no mention of any inhibitor checks on that list given that radiator corrosion causes a lot of problems in a heating systemIf it's a heating boiler here's an example of what's required from 1 manufacturer's manual,
although it would be much the same for a 3kw under sink water heater.
View attachment 101969
You have a leaking unvented system that may be because of an expansion problem thus making it unsafe, how can this be ignored as this is a potential safety issueUpdate:
I turned up, looked, saw it was a unvented system (that was leaking), took some pictures and drove back to office. It was then when I was told it was a safety check not a service (so why tell me service! ) and all he did last time was check rcd was working and a earth continuity check . So back I went and 10mins later done.
Surely a safety inspection of an unvented hot water system should include checking the functions of any safety thermo-stat and over pressure relief valve.
a failure of these devices could lead to an explosion.
Reply to Electric boiler service in the Central Heating Systems area at ElectriciansForums.net