Discuss Electric boilers - how is this going to work. in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
113
? Thinking ahead a wee bit here, it looks like lots of people will be switching from gas combi boilers to electric combi boilers over the coming years. Most of the electric boilers seem to be around 12kW, while most of the gas boilers I've seen even in flats and small houses seem to be 30kW plus. So my main question is, how is replacing a 30kW + boiler with a 12kW boiler going to be sufficient to heat the place?

Secondly, what to do about about max demand? Many old domestic properties have 60A or even lower cut-outs, so how does that work with a ~50A boiler? Do we have to get the DNO to upgrade (in my past experience they are very reluctant to do so). And what about other large loads like showers? Do we have to fit some kind of selector switch so only one can be used at a time?
 
I think we will see more ground and air heat pumps installed and instantaneous hot water systems in kitchens and toilets. Interesting thought about reservoirs of high potential electrons to cope with short term surges in demand. Or maybe families just pedal harder on their exercise bikes.
 
Interest times ahead. We all tried electric heating in the 70's, and people started ripping them out in the 80's. My son lived in a brand new modern all insulated all electric 2 bed flat, recently. His fuel bills were higher than our 80's 4 bed place, and he only heated his bed & kitchen.

Ground,heat pumps will be fine for new builds, think there's some forthcoming building regs for that, but what will I do with my defunct gas boiler in 10-20 years time?
 
My understanding is the same as Snowheads.

It's only new builds and TBH they are so well insulated these days the heating load is much smaller anyway.

Also Electric boilers are rubbish from my experience but at least they are simple.

ASHP seems to be more common for new builds here.

This is of course based on my limited experience of them I don't do that many new builds.
 
Interesting conversation! An electric boiler is probably not would I would choose for heating an all electric dwelling myself. Storage heaters would seem to make more sense with an increase in renewables as they lend themselves to demand-side balancing.

But, I've been working for a boiler dealer doing the wiring for mostly straight-swap gas boiler installations & heating controls, and he's asked me (I think hypothetically) about replacing a gas combi-boiler with an electric, hence my question. So is the consensus that this will not work? That electric boilers are only suitable for highly-insulated modern buildings? In the short term at least this would just be a house here and a flat there so not likely to have a big impact on the DNO network, but for the individual supply and installation it might be more of a problem.

Marconi, when you say 'reservoirs of high potential electrons', in practice does that mean capacitors? Is such a thing available to buy for this purpose (can't say I've seen one in the Screwfix catalogue!).
 
Generally the combis are 30+ kW in order to give decent hw flow rate. Electric boilers will most likely require a return to immersion tanks to even out electrical demand for hot water heating. A reservoir of high energy molecules...
Quite common to find system boilers in 12 to 18kW band.
 
Replace it with another gas boiler.
They aren't going to disappear, it's just that in the future new builds won't have Gas.

Heat pumps still need boost heaters to get water to 60, so it's unlikely the existing DNO network would support a street full of them.

Hmmmas Murdoch would say, not convinced thats going to happen
 
Generally the combis are 30+ kW in order to give decent hw flow rate. Electric boilers will most likely require a return to immersion tanks to even out electrical demand for hot water heating.

Starts to make sense. I mean, you'd never get close to 30kW with instantaneous electric heaters even with them all actually running and drawing current at the same time, except maybe in a mansion. So it seems like a system boiler and cylinder might be the way to go where an electric boiler is desired. The hot water could be set to run on low rate (night-time or when the wind blows/sun shines), while heating would be more on demand.

A reservoir of high energy molecules...

Think he's pulling our legs? ;):D:rolleyes:o_O

Quite common to find system boilers in 12 to 18kW band.
 
From personal experience I live in a 2014 apartment, the building is made of wood with a bath stone cladding.
the heating and hot water comes from a community heating system, they burn wood pellets on site and pump water to each apartment where a 'boiler' electric powered on a 16amp breaker reheats it.
my heating/hot water costs me between £20-22 a month.
This system apparently reduces the amount of energy lost in transportation and long cable or pipe runs.
I do think though that it wont be heating as we think of it now but will be a mix of solar powered, power wall to store excess and a modern version of storage heaters.
showers will be electric but there are new ones out there that operate at 20 amps which will be more than sufficient for most people. Think of ovens for years we were almost by habit thinking 40 amp and 10mm now im installing ovens on 20 and even 16amp breakers with 2.5 and even had one with a supplied 1.5mm cable.
things are going to change. necessity being the mother of invention and all that.
 
If they all had solar panels and storage batteries, that would surely help with the extra load...
That's the ideal solution... as in theory, if sized correctly, you could do away with your grid supply. I worked out the payback period of such a system for my place... but it was >20 years ! So at present, it's cheaper to use the grid supply.
 

Reply to Electric boilers - how is this going to work. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

My company has recently done some air source heatpumps which require DNO notification and EV chargers which also require DNO notification. On an...
Replies
8
Views
2K
Hi, my wife and I have decided to bite the bullet re the costs of an electric combi boiler in an off-gas grid one bedroom flat where space is so...
Replies
10
Views
2K
Good morning Guys Looking for some advice with regard to a current job. Building company I'm doing work for are installing...
Replies
2
Views
1K
I'm following a spark who used an existing Panel Heater circuit, for new gas boiler circuit 6 months ago. The panel heaters were removed, so it's...
Replies
43
Views
6K
Just looking at my boiler wiring out of interest, and just wondering if it's wired correctly. So perma lives, neutrals and earths in the right...
Replies
65
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock