Just looking at my boiler wiring out of interest, and just wondering if it's wired correctly.

So perma lives, neutrals and earths in the right place, but i can't figure out the switch lives to the controller.

If i follow the circuit it seems like the earth of the 4 core is acting as some sort of live to the controller even though the perma live is already there. If i volt stick it, the earth is live at both ends at all times, the black is showing 50v amperage only sometimes and then dead others.

From the wiring diagram i would have assumed the 4 core would go to the switch as L N E and the black would act as the sole switch wire.

What am i missing?

(Ps thanks for your help - i'm trying to get more into the domestic side of stuff having grown sick of site work so this is my first foray into stuff like boilers.)

PPS the controller is not a stat, it's just on/off. Timer/temp etc is built onto the boiler.
 

Attachments

  • 20230615_200727-min.jpg
    295.2 KB · Views: 49
  • 20230615_200731-min.jpg
    293.5 KB · Views: 48
  • 20230615_201329-min.jpg
    258.4 KB · Views: 48
Just because a wire is green/yellow doesn't necessarily make it an earth, especially if plumbers are involved!
Your controller is wired as 'volt free' , and the green/yellow has been used as a 'live'.
There doesn't appear to be a real earth at the controller, but it does look like there's one at the boiler.
 
Just because a wire is green/yellow doesn't necessarily make it an earth, especially if plumbers are involved!
Your controller is wired as 'volt free' , and the green/yellow has been used as a 'live'.
There doesn't appear to be a real earth at the controller, but it does look like there's one at the boiler.
The boiler is definitely earthed.

So could you talk me through the controller and what the '1' and '2' are doing on the boiler? I can't visualise how this works.

I gather the yellow/green is a live and the black is the switch, so what is the brown doing?

In my head, we have perma live in to boiler, out to controller. 240v out from boiler to the controller, button on controller than activates the black, turning the boiler on.

So howcomes the black is sometimes giving voltage sometimes not, when the controller switch isn't being operated?
 
Your boiler wiring diagram shows a link between two terminals at the top. This link has been removed and connected to the green/yellow and black wires, which, at the controller end, are connected to the switch terminals. The blue and brown supply power to the clock of the controller.
A five core cable should have been used, of course.
 
Your boiler wiring diagram shows a link between two terminals at the top. This link has been removed and connected to the green/yellow and black wires, which, at the controller end, are connected to the switch terminals. The blue and brown supply power to the clock of the controller.
A five core cable should have been used, of course.
Ah ok that makes sense - so the yellow is power in from the boiler, the switch is operated on the controller then the black switches the boiler on.

Still any idea why i'm getting a voltage reading now and again on the black without operating any switches? It seems to be intermittently going live but only registering 50v.
 
Fluke T90 which the spec sheet says 200kohms input impedance.

Interesting, you wouldn't normally expect that tester to display a voltage of it was due to capacitive coupling.

Does that model have the button to lower the input impedance?

What are you measuring the 50V with reference to? Is that 50V to earth, to neutral or something else?
 
Interesting, you wouldn't normally expect that tester to display a voltage of it was due to capacitive coupling.

Does that model have the button to lower the input impedance?

What are you measuring the 50V with reference to? Is that 50V to earth, to neutral or something else?
L to N is coming up 50v on the stick. It's the version that is just 'prod and play', without the button.
 
Wonder why they didnt take the timeclock live from the live output of the boiler, its a rare occurrence when the boiler switch terminals are actually marked in and out.
 
PPS the controller is not a stat, it's just on/off. Timer/temp etc is built onto the boiler.
That Honeywell R6660D is a wireless receiver, e.g. for a stat, intended to monitor room temp. Do you have the HCW80 or equivalent that goes with it?

I am puzzled by the 50V, but I'm afraid still a bit unsure exactly what you are measuring!
I guess the terminals in question (despite 2 being labelled 230V out) may be a control circuit, not necessarily directly connected to the 230V that's on the L terminal at the bottom.

If you are measuring terminal 2 wrt ground, I would expect 230V, given the label on the boiler, but if it's not that, it may be due to the source impedance of that voltage - though that seems unlikely given the 200k impedance of your probe.
Terminal 1 might assume any old voltage wrt ground with the R6660 off, as it's an input, and without the circuit diagram of the boiler, can't really determine.
If the boiler is working correctly, I think in the absence of a circuit diagram, you have to assume that terminals 1 and 2 are part of a separate control circuit not necessarily directly connected to the incoming mains, and be content that the voltages 'measured' don't indicate a problem!
Not if G/Y have been used for 'Live' conductors, therefore omitting earth connections and within cables.
The Honeywell R6660 is ClassII device and has no provision for an earth, so you might argue there's no safety issue other that the failure to sleeve this one cable etc. etc.?
 
Is there a fault with the heating, or are you just worried about the workmanship?
Nah was just having a look inside out of interest, boiler works perfectly - i just click the controller on and the boiler comes on, click it off for off.
That Honeywell R6660D is a wireless receiver, e.g. for a stat, intended to monitor room temp. Do you have the HCW80 or equivalent that goes with it?
It's supposed to be wireless? No other equipment i'm afraid, just that and the boiler. I was gonna get a smarter thermostat but can't justify a couple of hundred quid to do what i can simply do manually.
I am puzzled by the 50V, but I'm afraid still a bit unsure exactly what you are measuring!
When i just stick one pin of the voltmeter into the black i sometimes get 50v AC. On second thought it could just be the voltmeter showing that as part of showing an AC current since i wasn't measuring across more than one wire.
If the boiler is working correctly, I think in the absence of a circuit diagram, you have to assume that terminals 1 and 2 are part of a separate control circuit not necessarily directly connected to the incoming mains, and be content that the voltages 'measured' don't indicate a problem!
I don't think there's a problem i'm just trying to work out in my head how the circuit works - who said house bashing was easy!
The Honeywell R6660 is ClassII device and has no provision for an earth, so you might argue there's no safety issue other that the failure to sleeve this one cable etc. etc.?
Yep class II so no earth needed. Still poor imo to take the earth there as a live. Even some brown tape or anything woulda been better than just doing that.
 
Nah was just having a look inside out of interest, boiler works perfectly - i just click the controller on and the boiler comes on, click it off for off.

Disconnect it from the boiler terminals and see if this voltage remains at the boiler terminals.

When i just stick one pin of the voltmeter into the black i sometimes get 50v AC.

Then there's probably something up with your tester if it is displaying a voltage when only one probe is connected to something. You can't measure a voltage at a single point, it is always a measurement between two points.
On second thought it could just be the voltmeter showing that as part of showing an AC current since i wasn't measuring across more than one wire.

A voltmeter does not show current, it measures a potential difference in Volts. An Ammeter measures a current in Amps

I don't think there's a problem i'm just trying to work out in my head how the circuit works - who said house bashing was easy!

The circuit is a simple switch, a thermostat is just a switch which is operated by a change in temperature. When the temperature is lower than the set temperature the thermostat switches on and connects the two control terminals of the boiler together.
In your case the thermostat also has a permanent live and neutral supply to power it's electronics.

Domestic circuits, including heating controls, are at the relatively easy end of the spectrum.
Domestic installation work, or at least good work, is a skillset in its own right and can be hard as anything else.
 
It's supposed to be wireless? No other equipment i'm afraid, just that and the boiler. I was gonna get a smarter thermostat but can't justify a couple of hundred quid to do what i can simply do manually.
What you have is a wireless receiver, and back in the day would likely have had the HCW80 room stat paired to it somewhere in the house. Pic below in case you've seen that on the wall somewhere. It's battery powered.
It's been superseded by newer designs now, but you might pick one up on Ebay if you ever felt like it. It would need to be the old model to be able to pair it with your receiver.

The general view seems to be to replace with newer version if you need it, eg:


IMG_0166.jpeg
 
Voltage stick is as good as a chocolate fireguard, you need to measure it with a proper meter. Using g/y as anything other than earth does not comply with regulation and I’d advise you to get it fixed. Also, 50v is voltage, not amperage.
 
Voltage stick is as good as a chocolate fireguard, you need to measure it with a proper meter.
To be fair to the OP (see post #7) he is using a Fluke voltage tester, a lot more use than a chocolate fireguard.
It's not a 'proper meter', but safer as a basic tester than a cheap multimeter!
 

Reply to Is my boiler wired right? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
9
Views
270
I have a Firebird oil boiler that is controlled by a Honeywell timer (no thermostat) that has channels for hot water and central heating...
Replies
8
Views
440
Hi all. Yesterday I wired in my 3 phase compressor to run off our 53kva generator. I just need to know which colour cable is for which phase as...
Replies
13
Views
2K
Hi, I installed 6 recessed lights in my living room. I’m now up to the wiring part of the project. There is an outlet in the room that is...
Replies
1
Views
461
Had a new unvented Boiler fitted as the old one had reached the end of it's life. Electrician mentioned that it might be worth replacing my fuse...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock