Good morning everyone.
I have assignment now , but little difficult for me .
Any technical tutor Can to help me , I pay .
I send pictures now .
Thank you .
00E66E65-1940-4A89-A37A-6B0AB58C6DA6.jpeg
8483E731-1C84-4453-9A44-9F3A6E48D747.jpeg
DBFFD40B-473D-476A-A46A-2C8C701E740A.jpeg
44141D10-BF41-4CCE-9FDB-33742B5BFC04.jpeg
25845703-A119-4CB6-8D61-1E92D4749723.jpeg
EE209A2A-9118-49AB-B777-55844B808F70.jpeg
 
Unfortunately that’s not how we work on this forum. The best thing to do is to have a go yourself and then post your working out etc. At that point the members would be able to see where you are going wrong and steer you in the right direction.
[automerge]1571910627[/automerge]
We also have a trainee forum that you are more than welcome to join if you meet the criteria. Apply to Gain Access to Trainee-Only Forum - https://www.electriciansforums.net/forums/apply-to-gain-access-to-trainee-only-forum.60/
 
For me it highlights the problem within our industry, I don’t know what kind of course this lads on, but they should have taught him the formula and the process to carry out the calculations for design including correction factors. Not to mention the motor overload. Best thing to do is go back to your training provider, and ask them to explain what you don’t understand. You can’t really blag this stuff, it’s best to learn it.
 
For me it highlights the problem within our industry, I don’t know what kind of course this lads on, but they should have taught him the formula and the process to carry out the calculations for design including correction factors. Not to mention the motor overload. Best thing to do is go back to your training provider, and ask them to explain what you don’t understand. You can’t really blag this stuff, it’s best to learn it.
I wanna done but I can’t pay 300£ for assignment ?????
 
Talk to your tutor mate, you’ve already paid someone for this I’d assume?......between your course providers and the Internet these answers are are out there and easy to find.....it’s just a lot of hardwork/practice after that but if you are determined you’ll get there
 
OP, as already said, have a go at it and then post your answer, people will help then. You might know more than you think you do.

Don't feel too bad either, I know "Electricians" who would be embarrasingly stuffed with that paper,
The joke is, in my experience, half the so called sparks in the industry don't understand ADS properly and also the difference between fault and overload protection so it is important to learn it right.

It would seem, Select cable from CCC only with no rating factors applied, oversize it to allow for lack of design knowledge lol...... and hope the Zs is low enough for the PD. That is the standard design practice for many out there.

As for the adiabatic for sizing cpc's......very few out there can even do that.This is not reflected in people on forums such as this as if they are on a forum, they are generally more interested to even be on here in the first place.
 
Talk to your tutor mate, you’ve already paid someone for this I’d assume?......between your course providers and the Internet these answers are are out there and easy to find.....it’s just a lot of hardwork/practice after that but if you are determined you’ll get there
Do you know where get information for question 1 ,On suite guide or wiring regulation,I can"t see any information online .
question is State 5 sources of information which would help you design this installation .
 
Do you know where get information for question 1 ,On suite guide or wiring regulation,I can"t see any information online .
question is State 5 sources of information which would help you design this installation .
Best have a stab yourself and post what you think, members will comment on your answer and provide guidance....but wont answer the question for you.
 
Your calculation is correct but the answer is very badly wrong because you have put in some incorrect data through misreading the question. You have shown the efficiency as 0.75 % instead of 75% (=0.75) Therefore your answer is 100 times too large. Less importantly, 1 hp = 746W.

Think about what a motor of 0.75% efficiency would be like: It would waste almost the entire energy input. Also think about your answer of 1360A. The line and neutral cables to carry that would be as thick as your arms, yet the motor is no larger than the one in a good domestic pressure washer that runs on a 13A plug.

This is what we call a sanity check and it's worth doing every time. If the results of your calculation suggest that a cable must be 10000 km long or an electric shower will run on 0.01W, you can tell from real life experience that the answer is not sensible and probably indicates an error in the working or incorrect input data.
 
Last edited:
Best have a stab yourself and post what you think, members will comment on your answer and provide guidance....but wont answer the question for you.
I try but still difficult, I can’t find any information on Internet???
[automerge]1572951987[/automerge]
Your calculation is correct but the answer is very badly wrong because you have put in some incorrect data through misreading the question. You have shown the efficiency as 0.75 % instead of 75% (=0.75) Therefore your answer is 100 times too large. Less importantly, 1 hp = 746W.

Think about what a motor of 0.75% efficiency would be like: It would waste almost the entire energy input. Also think about your answer of 1360A. The line and neutral cables to carry that would be as thick as your arms, yet the motor is no larger than the one in a good domestic pressure washer that runs on a 13A plug.

This is what we call a sanity check and it's worth doing every time. If the results of your calculation suggest that a cable must be 10000 km long or an electric shower will run on 0.01W, you can tell from real life experience that the answer is not sensible and probably indicates an error in the working or incorrect input data.

What is the answer???
 
I try but still difficult, I can’t find any information on Internet???
[automerge]1572951987[/automerge]


What is the answer???

Lucien has explained where your mistake is. This should allow you to rethink how you calculated it. It's no good just giving you the answer.
 
Exactly! Use the same calculation, but with your efficiency as 75% and 746W/hp, and you will have the correct answer.

Are you on a course? If so, you should be able to turn to your tutor for advice when you get stuck, rather than relying on searching the WWW. The information is all out there but very spread out and not always accurate, whereas your course should provide, or direct you to sources (books!) of everything you need to complete assignments.
 
Lucien has explained where your mistake is. This should allow you to rethink how you calculated it. It's no good just giving you the answer.
Did you accept this answer????
Absolutely joke , I find professional company for assignment and doing all answers wrong now waiting for refund.
They put Volt-240 usually in Uk is -230.
In formula the same .
I’m very disappointed now .
 

Attachments

  • E1742B47-1333-4BF7-8C56-980E1A102E4D.jpeg
    100.6 KB · Views: 26
Did you accept this answer????
Absolutely joke , I find professional company for assignment and doing all answers wrong now waiting for refund.
They put Volt-240 usually in Uk is -230.
In formula the same .
I’m very disappointed now .

2.5 x 746 = 1865 Watts.
Which answer are you talking about accepting?
Edit: I may have misunderstood your post.
 
2.5 x 746 = 1865 Watts.
Which answer are you talking about accepting?
Edit: I may have misunderstood your post.
I talking about answer 7.77A why /240V , they need to used correct formula answer not 7.77A.????
 

Attachments

  • 18A06DFF-966C-4D74-8F24-0FF0A31954BD.jpeg
    60.6 KB · Views: 22
I do hope this is a wind-up!

You had a good stab at it, but made a simple mistake. I pointed out where that mistake was, so you could correct it. But you seem to have purchased 'answers' for your assignment from someone who knows less than you do. Have a bit of faith in your own abilities, talk to your tutor, fix your own answers and you'll be 100 times better off. Good luck with your refund.

BTW, When you are in hospital for life-saving heart surgery, ask yourself whether the surgeon actually studied heart surgery, or just bought their assignment answers from cash-strapped students overseas?
 
I wouldn't get hung up about the 230v issue - your calculation was wrong by a significant amount because of the percentage error.

Edit: is Lucien correct.? Did you buy these answers? You really need to try the question again yourself.
 
Did you accept this answer????
Absolutely joke , I find professional company for assignment and doing all answers wrong now waiting for refund.
They put Volt-240 usually in Uk is -230.
In formula the same .
I’m very disappointed now .
The quoted voltage isn't over relevant. The declared UK voltage is 230 -6%/+10%. This gives a range of 216.2 to 253.0v.
 
The quoted voltage isn't over relevant. The declared UK voltage is 230 -6%/+10%. This gives a range of 216.2 to 253.0v.
I wouldn't get hung up about the 230v issue - your calculation was wrong by a significant amount because of the percentage error.

Edit: is Lucien correct.? Did you buy these answers? You really need to try the question again yourself.
I try my self but I’m too busy all first 8 question is w
They need to by used this formula???
 

Attachments

  • AC157941-AD3C-4A43-B91E-70CB0FEF641F.jpeg
    57.1 KB · Views: 18
Looks like part of your message is missing, but I can see the part which says you are too busy to try it yourself. If this is the case then there really is no point in doing the course. Would you really be happy if you passed a course like this without understanding it?
 
Looks like part of your message is missing, but I can see the part which says you are too busy to try it yourself. If this is the case then there really is no point in doing the course. Would you really be happy if you passed a course like this without understanding it?
I try my self but still confused, that asking people for help ???
 
From Professional assignment electrical centre in London , the best one .
I’m very lucky pay just deposit.
I try to claim for Fraud now
??????

If you've got time to claim against this company then you've got time to try the question again. Why don't you want to do this?

Do you actually want to understand things fully, or just pass the course?
 
Your original question paper quotes the supply as 400v, three phase so you have 230v single phase. Ignore the 240v on your answers paper it is throwing you. Clear your mind and start again. Go back and read #15.
 
Your original question paper quotes the supply as 400v, three phase so you have 230v single phase. Ignore the 240v on your answers paper it is throwing you. Clear your mind and start again. Go back and read #15.
Thank you .
If you've got time to claim against this company then you've got time to try the question again. Why don't you want to do this?

Do you actually want to understand things fully, or just pass the course?
I wanna understand everything and pass the courses, I try the contact the assignment company but not answer all morning.
[automerge]1572958179[/automerge]
I can’t see any example assignment Level 3 , I spend lots of time in Google searches but nothing.
I explain before I’m not lazy ,I like this forum everyone is friendly.
But sometimes people need to be little push to continue the live .
If someone know the theory tutor to help me distancing should be great.
At the moment I work different types of jobs long day over 12 hour , I not have enough time for nothing.
I can’t doing any homework or see my family.
I waiting for Refund today .
Thank for everyone.
 
Last edited:
Just to clarify, what have you paid for (not the dodgy answers, the original course you are doing), and where are you doing this course? Do you have a tutor?

How much was the course out of interest? (don't answer if you don't want to).
 
I'm afraid something has to give, the course or your twelve hour working day as both are not panning out. You need to ask yourself is this course going to benefit your future prospects and if so something in your current working life has to give.
 
I'm afraid something has to give, the course or your twelve hour working day as both are not panning out. You need to ask yourself is this course going to benefit your future prospects and if so something in your current working life has to give.
I know, but that course for Adults because I can’t stop working at the moment, I can’t be pay my bills.
My wife is half time , when she start full time I try to get more Day off and learning for my courses.
I’m happy this forum.
But at the moment I make mistakes after mistakes and everything wrong .
I don’t know where the best way to start .
Just to clarify, what have you paid for (not the dodgy answers, the original course you are doing), and where are you doing this course? Do you have a tutor?

How much was the course out of interest? (don't answer if you don't want to).

Course is proper one Level 3 Diploma.(3500£)
One day theory, one day practice.
But assignment is individual, for everyone.
You know too hard , I asking people Electrical Clarkson Evans my Jobs they still can’t help me .
 
I do hope this is a wind-up!

You had a good stab at it, but made a simple mistake. I pointed out where that mistake was, so you could correct it. But you seem to have purchased 'answers' for your assignment from someone who knows less than you do. Have a bit of faith in your own abilities, talk to your tutor, fix your own answers and you'll be 100 times better off. Good luck with your refund.

BTW, When you are in hospital for life-saving heart surgery, ask yourself whether the surgeon actually studied heart surgery, or just bought their assignment answers from cash-strapped students overseas?
I nearly done question number 1,2 and 6 and 7 .
Can you someone give me advice or show me questions number 3 and 4 , Please???
 

Attachments

  • 80EDD1F8-FED6-4413-8B33-443486A07D08.jpeg
    85.3 KB · Views: 22
Good morning, and happy new year, to everyone.
I’m stuck again my assignment???
I nearly done half assignment but I can’t move any more .
I wanna help please???
[/QUOTE]
 

Reply to Electrical assignment Help ?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone Just looking for some advice and guidance on approaching my HNC in electrical engineering and bridging units. How did other people...
Replies
3
Views
658
Good morning all I have a summer assignment that I need to have ready before the 4th of September and I have 4 tasks that I have yet to complete...
Replies
0
Views
797
I'm unsure if I should be an electrician or maybe another trade is better. I have basically completed my first year of a foundation in...
Replies
9
Views
758
  • Sticky
  • Article
ANNOUNCEMENT: New Moderator Assigned: @Megawatt (Please congratulate!) @Megawatt has been a forum member for a while now, he's an American chap...
Replies
22
Views
2K
Hi to Everyone. Anyone has done a personal interface to communicate DLRO100H using SCPI commands? i´m using Visual studio2022 sotfware, and i´m...
Replies
0
Views
208

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock