lokesh.dee

HI

I have a MCC panel it is showing KW reading for each phase L1,L2 and L3 are 4.7KW,4.0KW and 4.2 KW repectively. the energy consumption for 2 hours was 16 Kwh.how come it is possible

my doubt is my load was stable for 2 hours with 10-15% variation i should be 8-10 Kwh for 2 hours why it is 16??do we have to consider sum of 3 phases power??? or average of them??
 
thank you!!

I am sure that it is K W . if it is sum it should be 24KWH for two hours right??!! because the load was stable for 2 hours
 
there is energy meter installed in the panel i wanted to compare the kw and kwh reading so i have asked this generel question

tell me in generel total KW of a motor = L1KW + L1KW + L1KW


if it is the case where we can find supporting theory??
 
While a 3 phase motor running which is connected to particular panel kw reading is showing only for one phase l 1. My doubt is on energy meter why that is showing only one ohase kw ??!!!
 

Reply to electrical energy calculation in 3phase in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Probably more of a maths problem than anything else / managing to confuse myself. I have been asked to look at energy consumption of some...
Replies
7
Views
559
Hello everyone In September 2023 I rented a beautiful 3 bedroom apartment, with all electric supply, no gas powered appliances. I noted down the...
Replies
16
Views
2K
I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
D
I understand how to calculate the current in the neutral conductor on an unbalanced three phase installation, however am struggling to grasp how...
Replies
14
Views
6K
I've been looking at a job installing a vehicle charging point on a commercial premises. Earthing facility is PME, installation is 3 phase. Now...
Replies
3
Views
2K
DuaneMHunt1976
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock