Andy M

Got a bit bored of the old threads, so i thought i'd throw this into the cooking pot!

Recently i was asked to perform some very menial minor repairs to a property, despite the fact that i didn't consider that re-lamping and re-fixing loose accessories an "alteration or addition" i checked for the usual earthing and bonding. Surprisingly the bonding had been done, However i discovered that the main earth had never been connected!! It was a TT system with no 100mA rcd at the front end or earth electrode. also the "meter" tails from the box outside were a piece of 25mm 3 core SWA and where the "sparks" who had wired it had stripped it back and it wasn't double insulated at the meter. My guess was a PME sorry TN-C-S had been requested at the time but no one ever followed this up. The Consumer Units didn't bear the culprits name and no test results were available. I have since correctly terminated the SWA into 100mA rcd (insulated enclosure)and installed an earth stake. Now the burning question is have i altered the "tails" swa into a disribution circuit, so only need a minor works, or as with a mains swap do i issue an Electrical Installation Certificate?

Your Thoughts would be appreciated
 
Got a bit bored of the old threads, so i thought i'd throw this into the cooking pot!

Recently i was asked to perform some very menial minor repairs to a property, despite the fact that i didn't consider that re-lamping and re-fixing loose accessories an "alteration or addition" i checked for the usual earthing and bonding. Surprisingly the bonding had been done, However i discovered that the main earth had never been connected!! It was a TT system with no 100mA rcd at the front end or earth electrode. also the "meter" tails from the box outside were a piece of 25mm 3 core SWA and where the "sparks" who had wired it had stripped it back and it wasn't double insulated at the meter. My guess was a PME sorry TN-C-S had been requested at the time but no one ever followed this up. The Consumer Units didn't bear the culprits name and no test results were available. I have since correctly terminated the SWA into 100mA rcd (insulated enclosure)and installed an earth stake. Now the burning question is have i altered the "tails" swa into a disribution circuit, so only need a minor works, or as with a mains swap do i issue an Electrical Installation Certificate?

Your Thoughts would be appreciated

An EIC for me as you have now added a 100mA rcd (s type hopefully) so have changed/relocated/added the mainswitch of the installation, so in effect making (as you say ) the tails from the rcd to cu a dist circuit.

But others may have a different take on it. :)
 
I'm afraid someone would say this, (i was trying to avoid another 3 page Certificate!) Out of interest how far would you go with the testing of the existing installation?
 

Reply to Electrical Installation Cert or Minor Works? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top