I'd appreciate some advice on an insurance dispute: Last year the electricity board sent someone to replace our 3 phase meter. He mis-wired it and popped anything electronic, any lights that were on, and a fair number of white goods. He left it mis-wired for about 15 mins and it didn't trip any house fuses. We never worked out exactly what he did, as his boss turned up to re-wire it, and neither me or the insurance company know exactly what he did. It may have been neutral loss or some other other phase wiring cock up.

I'm now approaching the end of a large insurance claim and one thing the insurer is resisting is the cost of repair to an electric underfloor heating cable that no longer works (the whole floor would need digging up). It was fine before, but now pops the RCD. The cable is two wire only, 2600w and the loop resistance is as per spec but there is a current leak somewhere. It's nothing house side of the cable, and has to be under the tiled floor.

I'm trying to understand the conditions that could have caused the insulation to melt or other possible damage? Any thoughts that can help me go into bat against the insurer are much appreciated.

many thanks
 
If the heating was on and the wiring was such that you had 400V instead of 230V on the heater (for example L2 and N were swapped over during the accident, with the heater is normally on L1-N) then it would be running at 3 times its rated thermal output (as power in a resistor is proportional to voltage squared) and probably would damage insulation some time before actually burning out the heating element. That could explain the RCD tripping on that circuit.

But it would require a bit more knowledge of the heating element and the type of insulation, etc, to know for sure if x3 heat would cause such damage.
 

Reply to Electrical insurance claim for broken underfloor heating 400v+ neutral loss? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Conversation developed with a middle aged lady who has recently lost her husband. Note to self, stop walking dog around the graveyard Anyway...
Replies
5
Views
1K
Hello Guys, I was wondering if any of you nice chaps could lend me some advice. So I have an open vented heating system with a 3 port valve...
Replies
11
Views
2K
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Replies
2
Views
743
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi all, Was speaking to a family member recently, he told me his iron recently made a bang and flash as he plugged it in to the socket, and could...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock