Discuss Electrical shock from extractor hood in the UK Electrical Forum area at ElectriciansForums.net

CTID71

DIY
Reaction score
8
DIYer here. Just purchased extractor to fit into chimney. Have fitted fused spur to downstairs ring main. Tried to test extractor by applying plug before fitting to fused socket. Worst thing I have ever done. Got a really bad shock while holding extractor. Have applied plug to extractor previously and never experienced anything like this. Can anybody assist me. Thanks in advance
 
Some pictures might help.
Thank you for replying. Instructions say Warning! This appliance must be earthed - think I have messed up here, item bought online - clearly Chinese import via Co based on Nottingham. Don't usually buy electrical appliances online and was hesitant. Feel I may need to Earth appliance but don't know enough abbot how to go about this.
 

Attachments

  • 1613214375058587283485423761689.jpg
    173.5 KB · Views: 81
  • 16132144182574164421604668620919.jpg
    328.4 KB · Views: 78
  • 16132144650419088389760296934109.jpg
    218.8 KB · Views: 81
You wired the plug incorrectly?
OMG. I think you have just answered the problem. Having thought about it. I think I connect the earth under the fuse. Not sure why. Socket I plugged into, tested and correct, Fuse box RCD protected. I want to try again with it on the floor and test to see if live when connected. Is this how you would go about it? Thank you for everything. First tinge I have posted on this site. I don't mind paying to get trades out but felt I could tackle this. Main issue being getting the cann thing fitted into chimney.
 
Picture of the inside of the 13amp plug showing how you connected it??
Can only remember from memory and talking to my daughter I may have connected earth beneath fuse in L spot. Would this have done it? Disconnected yesterday thinking lucky to be alive. Well actually not with the problems I am trying to plough through...Really appreciate you're reply and those of others. I am really grateful and this is a lesson learnt
 
He is in Lancashire, doesn't say what part of Lancashire though so he may not be too far from me if it is South Lancashire
To far for me what ever part of Lancs' the poster is from, sorry to say.
 
Brown is live!
Blue is neutral,
Earth is green and yellow
Congratulations @littlespark
you have just passed your online stage 1 exam from JSP school of training.
certificate is in the post.

Please send promptly your payment for module 2 (£1000)
course content,
  • screwdrivers, correct selection
  • advanced screwdrivers, identification of handle and driver tip
  • cutters, knifes and strippers, what they are and how to use them
  • advanced cutting, how to open a box, how to remove the cable tie on your new cutters.
  • FREE BONUS MODULE
  • Strippers, what should they cost?, how to operate, correct PPE, ergonomics and the correct way to hold your tool.??
P.s. If you have not become a qualified electrician after completing the first 50 modules in the course, i will discount the remaining 50 modules by 50%
 
Last edited:
It sounds like you had a lucky escape, and your family. As you say you were holding it I presume it went through your hands, via the heart. I strongly recommend you get a check up at the A&E dept for any harm it may have done. It can happen that damage is caused to the heart in such situations as you describe. Sorry if that sounds alarmist but I would take it seriously.
 
It sounds like you had a lucky escape, and your family. As you say you were holding it I presume it went through your hands, via the heart. I strongly recommend you get a check up at the A&E dept for any harm it may have done. It can happen that damage is caused to the heart in such situations as you describe. Sorry if that sounds alarmist but I would take it seriously.
good point, even a visit to the local GP, they probably have an ECG machine which is what they are going to test you with.
 
Red was a good colour for live. Denotes danger... brown could be confused as earth, because, well earth, as in dirt is brown??

Brown is live!
Blue is neutral,
Earth is green and yellow

Brown is live! (Repeat)

just covering my back.
Quality? Just had another great day. Covered incovered in soot moving a frame and then
Red was a good colour for live. Denotes danger... brown could be confused as earth, because, well earth, as in dirt is brown??

Brown is live!
Blue is neutral,
Earth is green and yellow

Brown is live! (Repeat)

just covering my back.
Brilliant.....
 
It sounds like you had a lucky escape, and your family. As you say you were holding it I presume it went through your hands, via the heart. I strongly recommend you get a check up at the A&E dept for any harm it may have done. It can happen that damage is caused to the heart in such situations as you describe. Sorry if that sounds alarmist but I would take it seriously.
Only today was thinking the same. Have fitted loads of plugs and can't believe I wired it this way. Never would have thought the repercussions would have been so bad.
....kind of noticed something but distracted and didn't pay it a great deal of attention. Has scared the hell out of me. Thanks for your concern. I may just do that. Had another great day moving the frame in the chimney, covered in soot then covered in bath water in dealing with an iced up pipe (never happened before). Having the time of my life at the moment.
 
Thank you for replying. Instructions say Warning! This appliance must be earthed - think I have messed up here, item bought online - clearly Chinese import via Co based on Nottingham. Don't usually buy electrical appliances online and was hesitant. Feel I may need to Earth appliance but don't know enough abbot how to go about this.
CDA is the in-house brand of Howdens.
They may or may not be chinese, but tend to be generally far better made then those of Cokee Lewis (They do not bother with earthing any more), Which still is superior to those sold in screwfix where warranty claim (after one month when By low its covered by shop ) requires you to send it to factory in HONG-Kong for assessment...
 
CDA is the in-house brand of Howdens.
They may or may not be chinese, but tend to be generally far better made then those of Cokee Lewis (They do not bother with earthing any more), Which still is superior to those sold in screwfix where warranty claim (after one month when By low its covered by shop ) requires you to send it to factory in HONG-Kong for assessment...
CDA is not the in house brand of Howdens like Cooke & Lewis is for B&Q. I work for 2 independent kitchen companies and have been connecting up CDA appliances for years, they are totally independent
 
CDA is not the in house brand of Howdens like Cooke & Lewis is for B&Q. I work for 2 independent kitchen companies and have been connecting up CDA appliances for years, they are totally independent
Accepted, I have done some checking and it seem to be a UK sub-company (with some UK manufacturing) of a polish company. That might explain why it is safer then Cokee
 
Last edited:
I used to like Beko before Dickson (Curries) bought and ruined it.
What it comes to is Lamona the original (Proper) Beko manufacturer (some Czech bloke, his son and few friends) that gave us things which take any misuse you throw at it or did it get ruined with Beko itself?
 
I used to like Beko before Dickson (Curries) bought and ruined it.
What it comes to is Lamona the original (Proper) Beko manufacturer (some Czech bloke, his son and few friends) that gave us things which take any misuse you throw at it or did it get ruined with Beko itself?

Beko was (and still is) a Turkish company, owned by parent company Arcelik. It has never been owned by any Czech bloke, with or without the help of friends and family, and has never been owned by Dixons Retail.

They also own Beko PLC - Beko's UK subsidiary.
 
Last edited:
Beko was (and still is) a Turkish company, owned by parent company Arcelik. It has never been owned by any Czech bloke, with or without the help of friends and family, and has never been owned by Dixons Retail.

They also own Beko PLC - Beko's UK subsidiary.

Yet all the good bekos I have seen had Made in Czech republic, All the rubish ones I have seen are made in Turkey, I didnt do the research. I may as well shut-up about corporate things...
 
Yet all the good bekos I have seen had Made in Czech republic, All the rubish ones I have seen are made in Turkey, I didnt do the research. I may as well shut-up about corporate things...

That's not related to the content of your previous post.

I haven't commented about where they manufacture products for various markets, nor the fact that white goods are often produced to slightly different specifications for large retail groups, but simply pointed out that Beko's owners were not whom you had stated.
 
I'm laughing now, but this thread frightened the wits out of me this morning.


Edit: Laughing stopped again as I noticed it's valentines day tomorrow. Dog house for me.
Wife didn't mind me skipping Valentine's after the weekend. Final straw this morning....Isolation valve forced off uninsulated water pipe in utility following low temperatures (Pennines). Flooded utility, blew the electrics. I'm just waiting for the next problem....
 
Yet all the good bekos I have seen had Made in Czech republic, All the rubish ones I have seen are made in Turkey, I didnt do the research. I may as well shut-up about corporate things...
Loz2754 remove your like it gives him a point to the Arms rating, I don't know where he gets this rubbish from.

Ziodej please do take your own advice, but apply it to everything not just corporate things.
 

Reply to Electrical shock from extractor hood in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

This isn't very electrical, but never mind! I'm adding an extractor fan to a bathroom in a 4th floor flat. The builder has helpfully cored a hole...
Replies
20
Views
2K
I experienced an electrical shock while replacing an A/C Fan Coil's 120vac, single phase motor that was above the ceiling grid in an office, while...
Replies
46
Views
4K
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Good afternoon all, today I experienced a near death electric shock. This happened on a single phase domestic property! I was carrying out a few...
Replies
15
Views
3K
Not specifically electrical, but best way to minimise condensation in a shower room. Asking for a customer. Background. Customer is a neighbour...
Replies
9
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock