Tonkolili

The company i work for manufactures machinery which have a control panel that houses all of the switchgear,inverters starters, PLCs etc, we carry out the electrical install on the machine but when it goes to the client, we are not responsible for the mains supply to the control panel, what i want to know is what are the regulations on testing the Earth Loop impedance etc on production lines. My opinion is that when we install the machine (when i say machine its actually a production line) we should carry out a full electrical test and inspection as you would on any installation, most of the circuits are Motors,Lighting,safety circuits and instrumentation. I have encountered this before where no testing is sort by the client or anybody when installing machinery, it seems to be the opinion that it is just the fixed wiring of a building that requires testing ??? any comments would be appreciated
 
Whoever installs the supply will cert' it for compliance, whoever installs the machine only need to clarify before energising that everything is sound and Zs is good of the supply as is the duty of anyone energising a new install, although I'd recommend there be a section in the commisioning paperwork to confirm its been checked and passed.

The machine supply is classed as part of the fixed wiring of the building so like all circuits it requires testing, the equipotential bonding and earthing of the building also requires confirming.
 
Last edited:
Are you asking if you can apply 7671 after the isolator on your 'machine' exactly like you do on the fixed wiring?

If so the answer is no, it's not possible to calculate or measure the EFL through the DC bus on a VFD. The manufacture will guarantee a disconnection time under fault. Ask them.

Circuits that are DOL can be as you can get the tripping curves for motor overloads from the manufacture such as Telemec/Schneider overloads.

Cable CCC's and installation methods can also be lifted from 7671 but 60204 needs to be your main focus.
 
I know I wouldn’t like to get the machine going after someone had tried testing to BS7671 compliance. Testing the supply is about it.
 

Reply to Electrical testing on Machines in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi all, I am an electrician working for a OEM machinery manufacturer based in Germany, we are the local hub that is now taking over the...
Replies
8
Views
1K
Morning all, We are looking at qualification requirements for inspection and testing to BS EN 60204, all of our work is past the main isolator of...
Replies
2
Views
754
I start my BTEC Level 4 HNC Diploma in Electrical & Electronic Engineering in the new year, what book do you recommend to get to help me with my...
Replies
1
Views
675
Hello everyone, Hope you're all well. I'm carrying out an overall/global insulation resistance test on a newly wired 3 phase installation we did...
Replies
24
Views
1K
I've been retired a few years now so no longer active in the industry, but I've been doing electrical "stuff" for most of my life. Trained as a...
Replies
3
Views
373

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top