Hi everyone,

I have a job tomorrow where I have to replace some old non maintained, non functioning emergency luminaires in a church hall. They currently have no key switch test facility so I also need to install this. Is it acceptable to install the key switches next to the consumer unit serving the lighting circuits from which the ELs are fed, to interrupt the supply to said circuits (normal lighting included), or is it preferrable to install local key switches to each luminaire? (Alot more work!) Worried about the implications of interrupting the normal lighting while testing ELs.

Cheers
 
There must be 2 existing permanent feeds, one supplying the light switch, and one supplying the emergency light....both are either connected to the mcb, or linked across the light switch. So either fit keyswitches at db board, or fit dual switch/keyswich at existing light switch.
 
There must be 2 existing permanent feeds, one supplying the light switch, and one supplying the emergency light....both are either connected to the mcb, or linked across the light switch. So either fit keyswitches at db board, or fit dual switch/keyswich at existing light switch.

Unless it's like one of my regular customers where the feed just goes from MCB to em light to switch to next switch to em light etc etc (conduit and singles) so we can't seperate them out without significant alterations.
 
There is a unit inside, which you preset the test timer, say 6 months.....the unit dissconnects the battery, and tests it. At the same time it measures the light intensity of the lamp. if battery or lamp fail, a red led comes on.
 
There is a unit inside, which you preset the test timer, say 6 months.....the unit dissconnects the battery, and tests it. At the same time it measures the light intensity of the lamp. if battery or lamp fail, a red led comes on.

The staff still need to spot and act on the flashing red led. I spotted two in a branch of a well known national spiced chicken restaurant and the manager thought it was something to do with the heating. A note went into head office, and I have been offered a free meal. I suspect the oversight was repeated across their whole estate....
 
The staff still need to spot and act on the flashing red led. I spotted two in a branch of a well known national spiced chicken restaurant and the manager thought it was something to do with the heating. A note went into head office, and I have been offered a free meal. I suspect the oversight was repeated across their whole estate....

Thats the problem....Advanced make an addressable em monitor, which is just like a fire panel. it test battery an lamp at preset dates, and zones. Then either displays or prints results. Used a few in large train stations.
The High Performance Emergency Lighting Test Panel - Lux Intelligent
 

Reply to Emergency lighting key switch in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
665
Hi all Got a question regarding HMO compliance. Visited property today for landlord looking to apply for an HMO license for one of their...
Replies
5
Views
1K
Two lighting circuits covering various communal areas on two floors of a HMO. The non-maintained emergency lighting that covers those areas is on...
Replies
18
Views
2K
Hi, RCBO appropriate test facility for emergency lighting? I have a car storage facility ( one corridor with 10 rooms off the corridor to store...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock