Hi all,
This is kind of prompted by the existing emergency lighting thread, but is subtly different.
I do some work for a charity in Cardiff and on my last visit I was asked to investigate the failure of a light in a toilet. Turns out, it's an emergency luminaire that uses a couple of CFL lamps and a high frequency electronic ballast/charger/inverter unit.
It simply didn't work at all under any circumstances. I investigated and I believe the problem was caused by a failed electrolytic cap on the ballast board. The batteries were also shot and didn't appear to be holding any form of charge.
Further investigation revealed another unit in a similar state.
I've purchased new ballast units designed for this purpose along with new battery packs and have rebuilt one unit and am going to do the other on-site. They are the same spec in terms of operation and run time. Aside from the obvious electrical and operational checks, as these are emergency lights do I need to do anything other than repair and replace as I'm not changing operation, run time, illumination levels or anything, I'm just bringing them back into service?
Just don't want to end up on the wrong side of the rulebook as it's a charity and effectively a public building.
Thanks
This is kind of prompted by the existing emergency lighting thread, but is subtly different.
I do some work for a charity in Cardiff and on my last visit I was asked to investigate the failure of a light in a toilet. Turns out, it's an emergency luminaire that uses a couple of CFL lamps and a high frequency electronic ballast/charger/inverter unit.
It simply didn't work at all under any circumstances. I investigated and I believe the problem was caused by a failed electrolytic cap on the ballast board. The batteries were also shot and didn't appear to be holding any form of charge.
Further investigation revealed another unit in a similar state.
I've purchased new ballast units designed for this purpose along with new battery packs and have rebuilt one unit and am going to do the other on-site. They are the same spec in terms of operation and run time. Aside from the obvious electrical and operational checks, as these are emergency lights do I need to do anything other than repair and replace as I'm not changing operation, run time, illumination levels or anything, I'm just bringing them back into service?
Just don't want to end up on the wrong side of the rulebook as it's a charity and effectively a public building.
Thanks