Discuss Emergency Lighting Tests - should normal lights go off? in the Lighting Forum area at ElectriciansForums.net

S

Slowbutsure

Hi There

I work on a large Government site with 500+ emergency lights, both maintained and non-maintained. Some of the emergency lighting circuits are wired so that upon carrying out a key switch test the normal lighting goes off.

But there are some emergency lights where the normal lights stay on during a key switch test. So I am trying to establish if the normal lights should go off during a key switch test or not. The 17th Ed. wiring Regs do not say much so I went and bought the IET guide to Emergency lighting but this also did not clarify if normal lighting should stay on during a key switch test!

Can anyone clarify?
 
I believe the approach now is that normal lighting should not go off when the emergency lighting is being tested as this could cause danger if the testing is being done during working hours.
However this was not always the case and often EM lights were wired so that the whole lighting circuit was powered down on operating the test switch. (and quite often I have seen EM lighting where the lighting MCB is used as the test switch! simple but not sensible)

If you have an installation where the normal lighting goes out then you have to take this into consideration when testing.
 
As your already aware - The key switch is provided to put the emergency luminaries into emergency mode for testing purposes. It might be preferential to have the non-emergency luminaries remain on during this test but it isn't a requirement. Bs 7671 won't be particularly helpful to you, try bs 5266-1 2016. 5266-1 also has guidance on testing procedures which may benefit you. Thanks
 
I believe the approach now is that normal lighting should not go off when the emergency lighting is being tested as this could cause danger if the testing is being done during working hours.
However this was not always the case and often EM lights were wired so that the whole lighting circuit was powered down on operating the test switch. (and quite often I have seen EM lighting where the lighting MCB is used as the test switch! simple but not sensible)

If you have an installation where the normal lighting goes out then you have to take this into consideration when testing.

Thanks Richard - I will check the installations, maybe the difference is between occupied and non-occupied areas.
 
Creating a dangerous environment due to the activation of a test is not advisable. A review of the buildings o and m manual should reveal when it was originally designed to be tested i.e. Out of hours, this might also give the installation time to recharge before reoccupation. If a full duration test is allowable during occupation you should be considering whether there is sufficent energy remaining in batteries to facilitate a successful evacuation.
 
BS5266 will provide no guidance and never has on this, only that some means of test facility is provided. Some believe that a test facility interrupting the general lighting provides a realistic scenario for the effectiveness of the emergency lighting, this is nonsense as the test facility is there to test the operation of the fittings and no more. In some cases loss of general lighting is not too much of a problem but it can also pose a real risk to persons in an occupied premises. The use of a mcb for the testing is not acceptable for compliance with BS5266. I suspect that this along with a vast majority of emergency lighting installations in this country has been installed and tested by persons who do not have copies of the relevant BS5266 standards and hence have no understanding of the systems.
 
That is not true. BS 5266-1:2011 explicitly states that the test facility MUST NOT interrupt the normal lighting.

BS5266 will provide no guidance and never has on this, only that some means of test facility is provided. Some believe that a test facility interrupting the general lighting provides a realistic scenario for the effectiveness of the emergency lighting, this is nonsense as the test facility is there to test the operation of the fittings and no more. In some cases loss of general lighting is not too much of a problem but it can also pose a real risk to persons in an occupied premises. The use of a mcb for the testing is not acceptable for compliance with BS5266. I suspect that this along with a vast majority of emergency lighting installations in this country has been installed and tested by persons who do not have copies of the relevant BS5266 standards and hence have no understanding of the systems.
 
"8.3.3 Test facility
"Each emergency lighting system should have suitable means for simulating
failure of the normal supply for test purposes (i.e. without interruption of the
normal supply).
"NOTE An automatic test system for battery powered emergency lighting is specified in BS EN 62034."


It is worth noting that BS 5266-1:2016 was recently published which has altered the wording displayed in BS 5266-1:2011 (above). So it may not be a requirement any longer although I will have to have a proper read through the new Standard to verify that.
 
Now you have worded it this is familiar, got new copy somewhere but I wouldn't have thought it has changed.
 
Now you have worded it this is familiar, got new copy somewhere but I wouldn't have thought it has changed.
The wording definitely has changed, but I don't have my copy of BS 5266-1:2016 on me at the minute so can't post the new wording.
 
It used to be only in licensed premises such as cinemas, clubs, pubs, etc.
Anywhere that it would be expected to be dark during normal operation.
Now I understand that it is also in schools, hospitals, courts, etc.
Places where it would not be expected to be dark during normal operation.
 
Creating a dangerous environment due to the activation of a test is not advisable.

I accidentally killed the lights in a busy hotel kitchen once on an Inspection.
I got a surprisingly friendly warning form the head Chef (considering what some of them are like), that I should've warned them of the possibility, and I'd've been in deep whathaveyou if someone had chopped one of their fingers off.
Advice taken, understood and absorbed.
 

Reply to Emergency Lighting Tests - should normal lights go off? in the Lighting Forum area at ElectriciansForums.net

Similar Threads

Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
614
Hi Guys I've fitted a few emergency lighting circuits to both domestic and commercial installs before, I've come across one I can't get my head...
Replies
19
Views
1K
Hi, RCBO appropriate test facility for emergency lighting? I have a car storage facility ( one corridor with 10 rooms off the corridor to store...
Replies
12
Views
1K
Hi all Got a question regarding HMO compliance. Visited property today for landlord looking to apply for an HMO license for one of their...
Replies
5
Views
1K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock