Discuss Enclosure for 30ma rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Been out to a property to price up repair on a couple of little bits with an old wylex board which has a 100ma RCD main switch. If I was to fit an upfront 30ma rcd before the main board would it have to be in a metal enclosure, haven't needed to do this before and not sure if enclosure would have to be metal or plastic

Thanks
 
I advised a board change would be better but as this is a rental property & landlord does not want to spend would it not be better to make it safer with a 30ma rcd first

It may be safer it terms of increased protection against shock, but may be less safe in the event of a fault due to a complete loss of power. That's why there are regulations to prevent the action you are considering.
 
I advised a board change would be better but as this is a rental property & landlord does not want to spend would it not be better to make it safer with a 30ma rcd first

There is no regulation which allows you to ignore the other regulations when your customer wants to do a job on the cheap.
If the customer won't pay for the job to be done properly then turn the job down.
 
Some of that can be deemed maintenance but if you are moving the fan then additional rcd protection will be required, is it not suitable for use in zone 1.
 
Been out to a property to price up repair on a couple of little bits with an old wylex board which has a 100ma RCD main switch. If I was to fit an upfront 30ma rcd before the main board would it have to be in a metal enclosure, haven't needed to do this before and not sure if enclosure would have to be metal or plastic

Thanks
The guidance on this I was given is a plastic enclosure is acceptable as it doesn't fall into the category of similar switch gear assemblies as a consumer unit would.
Bit of a grey area still I think but the guidance seems to be that if it was TT you can have a upfront time delay 100mA in a plastic enclosure before entering a metal consumer unit.

Change the consumer unit tho rather than fit an upfront rcd protecting the whole installation
 
Similar switchgear assemblies

The phrase ‘similar switchgear assemblies’ in Regulation 421.1.201 means assemblies used for the same fundamental application as a consumer unit. A consumer unit is defined in Part 2 of BS 7671 as: ‘Consumer unit (may also be known as a consumer control unit or electricity control unit). A particular type of distribution board comprising a type-tested co-ordinated assembly for the control and distribution of electrical energy, principally in domestic premises, incorporating manual means of double-pole isolation on the incoming circuit(s) and an assembly of one or more fuses, circuit-breakers, residual current operated devices or signalling and other devices proven during the type-test of the assembly as suitable for such use.’

An example of a similar switchgear assembly is a three phase distribution board intended to be operated by ordinary persons. This would have to have isolation that interrupts the three incoming line conductors and the neutral, rather than just double-pole isolation as mentioned in the above definition.

Was sent to me via email from our QS whom sought guidance on the matter.

So depends if you think a stand alone rcd fits the bill.
 
What is all this fuss then about separate rcd enclosures on TT not being permitted, not my words unless in metal enclosure.
 
What is all this fuss then about separate rcd enclosures on TT not being permitted, not my words unless in metal enclosure.
I know wylex brought out an installation guide via YouTube when the new regulation came in about non combustible consumer units in which they brought out an s type 100mA rcd unit to fit into a plastic enclosure for use on TT installations.
Think the on site guide mentions an upfront time delay as an option as well as class 2 glands where the tails enter the consumer unit I'd have to check that tho.
 
The guidance on this I was given is a plastic enclosure is acceptable as it doesn't fall into the category of similar switch gear assemblies as a consumer unit would.
Bit of a grey area still I think but the guidance seems to be that if it was TT you can have a upfront time delay 100mA in a plastic enclosure before entering a metal consumer unit.

Change the consumer unit tho rather than fit an upfront rcd protecting the whole installation
Thanks for the advice Ian, I haven't needed to do this before and probably won't again but landlord didn't want to spend on a board change and that's why I posted for advice, I fully understand a single rcd protecting the whole install is not ideal but I wanted to make sure the install was safer and would rather not have lost the job, I did speak with napit technical this morning explained everything i was doing and he said as I wasn't making any additions or alterations I didn't need to do anything about the main switch being 100ma but if I did put an upfront rcd in I wasn't making the install any less safe.
 
The guidance on this I was given is a plastic enclosure is acceptable as it doesn't fall into the category of similar switch gear assemblies as a consumer unit would.
Bit of a grey area still I think but the guidance seems to be that if it was TT you can have a upfront time delay 100mA in a plastic enclosure before entering a metal consumer unit.

Change the consumer unit tho rather than fit an upfront rcd protecting the whole installation
Thanks for the advice Ian, I haven't needed to do this before and probably won't again but landlord didn't want to spend on a board change and that's why I posted for advice, I fully understand a single rcd protecting the whole install is not ideal but I wanted to make sure the install was safer and would rather not have lost the job, I did speak with napit technical this morning explained everything i was doing and he said as I wasn't making any additions or alterations I didn't need to do anything about the main switch being 100ma but if I did put an upfront rcd in I wasn't making the install any less safe.
 
bit of work with a jigsaw needed. amd. 3 compliant.


upload_2017-7-12_20-2-8.jpeg
 
I know wylex brought out an installation guide via YouTube when the new regulation came in about non combustible consumer units in which they brought out an s type 100mA rcd unit to fit into a plastic enclosure for use on TT installations.
Think the on site guide mentions an upfront time delay as an option as well as class 2 glands where the tails enter the consumer unit I'd have to check that tho.
Not disagreeing Ian in fact the opposite because there was such an issue about this when Amm.3 came out about giving tails fault protection with the separate rcd issue.
 

Reply to Enclosure for 30ma rcd in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
303
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
Hi all. Looking to refresh the MCB and RCCB (100A 30mA) units to my 20 year old Contactum P12/100N CU installed in my house. I have presently a...
Replies
2
Views
281
Quick question. I want to put an isolating 2p switch on my incoming supply from the meter to the board. I want this to allow easier board changes...
Replies
8
Views
821
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock