I did the Enecsys micro inverter training but they've got a technical hole in what they're offering???
They state that you can only connect a maximum of 16 micro inverters to one 30mA RCD so at 190w 16 panels is 3kWp so if we want 4kWp then we need 2 AC buses and 2 RCDs and unless we're doing some RCD schenanegans on the inverter side of generation meter then it won't work. Either way the pictures in the training materials don't look right.
They also show the lockable AC isolator at the wrong point in the circuit, the lockable AC isolator has to isolate the entire AC circuit including the generation meter.
Does anyone out there use these inverters if so how do you wire them up?
They state that you can only connect a maximum of 16 micro inverters to one 30mA RCD so at 190w 16 panels is 3kWp so if we want 4kWp then we need 2 AC buses and 2 RCDs and unless we're doing some RCD schenanegans on the inverter side of generation meter then it won't work. Either way the pictures in the training materials don't look right.