dmelec

Recently carried out an eicr on a property. whilst looking around the property i couldnt see any earth connection to the incoming water or gas. But carrying out a continuity test with my r2 lead it proved there was continuity to the incoming gas pipe and incoming water from an outing going 10mm Earth cable. Is this sufficient for a satisfactory?

Thanks
 
I assume you are talking about bonding to incoming metallic services.
You have been unable to find accessible bonding connections near the point of entry of these metallic services.
However you have a 10mm² cable in an unspecified location that has continuity to both water and gas incomers.

Does this 10mm² cable connect back to the MET?
Do you think it may connect to either the gas or the water incomers?
Can you see, but not reach, any bonding connections?

Overall this sounds unsatisfactory as there is no definite bonding in place. This is a critical safety measure and should not be guessed.
If there is bonding then it is not accessible and you cannot confirm it is labelled.
I might tend toward further investigation required as lack of dismantling / damage prevents confirmation of bonding.
 
Recently carried out an eicr on a property. whilst looking around the property i couldnt see any earth connection to the incoming water or gas. But carrying out a continuity test with my r2 lead it proved there was continuity to the incoming gas pipe and incoming water from an outing going 10mm Earth cable. Is this sufficient for a satisfactory?

Thanks

Hi, yes the earth does go back to an met, i suspect there is a connection to gas and water under floor but i'm unable to access it as its a finished house. I would normally run a new bond if it doesn't cause too much damage. in this case it means running a cable all the way round the front of the house to the gas meter and then on further to the incoming water and wouldn't look easy on the eye
 

Reply to Equipotential bonding to incoming gas and water in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
1K
Hi, I'm having a new boiler fitted in a new location. I need to provide power for the boiler which I'm looking to do myself. Boiler: Ideal Logic...
Replies
11
Views
2K
Please can someone explain if this is a TNCS or a TNS earthing arrangement because it looks like both to me. Old undersized main bonding conductor...
Replies
5
Views
2K
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
2K
I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock