Currently reading:
equipotential bonding

Discuss equipotential bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

tigerpaul

-
Arms
Reaction score
101
Just done a periodic, and found the water main bonding is daisy-chained off of the gas main bond.

I seem to remember thats okay as long as the cable is unbroken at the first point of call. ( g/y sleeving stripped back at the earth clamp )

However the cable IS cut and then both ends are crimped and the lugs bolted to the earth clamp.

Looking through the regs I cant find the actual regulation that forbids this... or is it okay but just bad practice??
 
Its right there in 411.3.1.2

Extraneous conductive parts must be connected to the MET.

In the case you mention the gas is connected to the water.

If it was one continued (unbroken) length then technically they are connected directly to the MET.
 
Can`t remember how many times I`ve seen this exact situation.

The easiest way to rectify it is to join the two pieces together with a 10mm butt splice crimp and strip the cable a few inches away and pass it though the termination on the clamp.
 
I didnt think there was a requirement for the conductor to be unbroken in the 17th.

Anyone got theirs handy to check?


I just did the 17th this week,
and we were told that it was ok to loop betweenn the main Gas and water.
BUT it had to be unbroken cable all the way to the last point wether it was gas or water

Richard
 
Indeed and thats how its also been for many years.

However, in past OSG's in has stated this with the pictures etc, but in the 17th, i dont think its mentioned anymore.

That what i was wanting someone to check as im not with my books at the mo.
 

Reply to equipotential bonding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock