Got one of these to install shortly ........ what caught my eye when I read the spec was:

"The controls for ovens and hobs are neatly housed behind the upper left door. And, of course, with no flue needed, your 990 EL can be positioned wherever you want, provided there’s a 2 x 13amp power supply."

Anyone installed one of these?

I was wondering about the 2 x 13A - would a standard 2 x 13A (i.e, 20A) socket be OK? The technical info just says 2 a 13A!

I've got the existing 6mm outlet to adapt so my initial thought is a standard 2G socket

Thoughts?
 
depends on the load(s) after applying diversity. as long as they total<20A a 2 gang socket would be OK. and does the appliance come with fitted BS1363 plug tops?
 
I think I would go for two single sockets. As I understand it single or double are rated at 13a. Although I understand diversity applied would bring that down, but then I don't know what the rating of each item is.
 
You could always chop the plugs off :)eek:) and use a dual outlet plate.

Edit; the smiley should be :eek:

Edit, edit. Cancel that manufacturer says use plug tops :oops:
 
Last edited:
Fun while working is good!
This one would be fun. Just had a look at specs (resting today) and it weighs in well over 300kg, my back feels worse just reading about it. It's not clear to me what the power needs are, but my best bet is there are 2 plugs, one for the cooktop and one for the ovens, each capable of 13A draw.
 
I made an enquiry into the ESSE EL 13's power consumption to ESSE technical department. Please see an extract from an email I received from their R&D section:

'We’ve been running some power consumption tests on the EL cookers.

The first being power consumption when on slumber over a 24 hour period.

The EL13 used 7.8kwh which equals to 0.3kwh per hour.

The 990EL used 10kwh which equals to 0.4kwh per hour.

The next test we ran was for the EL13 power consumption turning the Hot plate to full, the top oven to 200°C and the bottom over to 180°C from slumber and then left at these new settings over a 24 hour period.

It used 31.18kwh which equals 1.3kwh per hour average.'

I think you would be fine plugging an EL13 into a double socket of a good brand since the averaged power consumption is around 0.4kW in slumber mode and 1.3kW for a representative use case drawn from two 13A outlets.

I hope this helps you make up your own mind.
 

Reply to ESSE 990 Electric Stove .. in the Electrical Appliances Forum area at ElectriciansForums.net

Similar Threads

Hi all, we had our gas hob removed months ago and finally just got round to putting an induction hob in. Its a normal 4 ring induction but one of...
Replies
3
Views
810
Hello All, I have just found out that a family member who is having some Building work done has been advised to insulate above the Kitchen...
Replies
16
Views
847
Hello everyone, Back again after receiving great advice for the bathroom a few months back. This time I'm making a mess in the kitchen. We have...
Replies
1
Views
1K
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
Came into work today with a fairly urgent requirement to install an instant hot water handwash unit in a small commercial kitchenette/servery -...
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock