Looking at installing 2x double EV charger units in an underground car park each unit requires 64A supplies, the nearest fuseboard is roughly 120m away

What would be the best option, installing a local DB near the chargers and running 2x smaller SWA's to the units or installing 2x larger cables from the far DB. Would it also be wise to install a 3P DB local to the chargers and supply the chargers from different phases, looking at cable sizes it would require 35mm2 to supply each charger from the far DB. What size cable would be needed to feed a new DB next to the EV chargers? Would you calculate it from 128A or 64A and put each charger on a different phase?
 
My advice would be a 3 panes sub main to nearby then if single phase a 4 core 6mm or 10mm and split over 2 phases

Three phase then 16 mm to each

What Make of points ?
 

Reply to EV Charger supplies in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m wondering if anyone would be able to tell me if I have a looped supply in my property as I’m looking to install an EV charger.
Replies
4
Views
276
I would like to hide the cable to an EV charger. The consumer unit, meter cabinet and charger would all be on the same wall. About 5 metres from...
Replies
19
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
752
Hi All, Im quoting to install an EV charger (Dont worry - fully registered, but only been 2 weeks so i'm still picking bits up). Consumer unit...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock