I am considering fitting a car charger using 6mm SWA to a new isolator switch in the meter cupboard and then 6mm T&E to the CU. It would save running the SWA all the way to the CU. Does anyone else do this and if so, which isolator is best for SWA? Thanks
 
All depends on which charger, some require RCD protection others do not and a double pole MCB would be suited. assuming you need type a rcd protection then the best option would be a double pole RCBO
I often install ev chargers by splitting the tails in the meter cabinet using a henley block, then fit a small consumer unit/ din rail enclosure with the most appropriate protective device ie RCBO, DP MCB or Main switch and SP/MCB all depends on the install, space and charger. I vary it as sometimes the preferred enclosure is not available or space tight so use what suppliers have.
A pitfall is to check if customer will be getting a smart meter fitted, if so ensure you leave space in the cabinet, not usually a problem if you plan it well and keep the tails tidy, flexi 19 strand tails are your best friend in this case.
 
in reply to your original post, 6mm may be ok, we dont know the load yet so cant comment.
there is no problem using twin and earth to an isolator and then swa after that.
just do your calcs for the two runs separately.
obviously ensuring that the total vd is within limits and that your earth will be sufficient (earth with armour or spare core? also remember that twin and earth has a reduced size cpc)
 

Reply to EV charger SWA isolator switch in the Electric Vehicles Advice Forum area at ElectriciansForums.net

Similar Threads

I have a client who wants an EV charger installed, charger TBC, but about 7KW, installed about 20m away from this installation. I've not done one...
Replies
37
Views
4K
I am an NICEIC contractor but I have never installed an Electric vehicle charger. I have watched all of the relevant NICEIC webinars (The wire) on...
Replies
18
Views
1K
I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at...
Replies
34
Views
2K
On another forum for general EV chat this question comes up all the time. It's very common to install a charger taking the supply direct from the...
Replies
14
Views
2K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
605

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock