Search the forum,

Discuss Ev point on a new build in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
37
Morning chaps
I’m starting two new builds next week and they’ve added a vehicle Charging point to each house,
Do I feed this via a 6mm t&e from the main cu or have a separate cu for it on an A type RCD?
I’ve not done my Ev course yet as it’s been cancelled 3 times due to corona and plus there isn’t a lot of call for it where I am at present, I think someone else who is olEv registered will be second fixing due to the builder getting a grant which I can’t offer.
I just want to know how best to tackle first fix.
thanks chaps
 
I would probably put in a swa cable (6mm 7kW?) on a mcb then the EV installer can put in the correct RCD protection in on their equipment.
 
I would probably put in a swa cable (6mm 7kW?) on a mcb then the EV installer can put in the correct RCD protection in on their equipment.
Hi thank you, I’m installing an rcbo board so would I run the armoured from the main Cu not a separate one on a 40amp mcb rather than an rcbo?
 
Some Ev points have fitted RCDs so only a MCB required if in SWA
Some require a separate Type A RCD fitted and MCB so a RCBO at DB is way forward
If in twin and earth then RCD protection will be required if buried in walls etc
 
You need to know the make and model of the EV unit, also requirements for earth electrode etc.
 
I would first check to see what charger is bring fitted. Then decide if you are fitting an mcb or rcbo... Some such as the Zappi or Andersen A2 only need an MCB the Zappi has built in type a the A2 has built in type B.
All depends on cable route of course.
Also consider the earthing. Some cheaper chargers need a rod or o-pen device. Higher spec such as those i mentioned do not and can use PME
 

Reply to Ev point on a new build in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock