Discuss evening from Scotland- advice if possible. in the The Welcome Forum area at ElectriciansForums.net

It could be done but most smart controls are designed for wet central heating systems rather than economy 7 hot water controls.
 
The only one I'm familiar with that could do the job is the honeywell evohome system as it needs to switch a 3kw load but that really is overkill.

What are you trying to achieve?
 
I had a look at this previously and I may be reading it wrongly but I reckoned this was for a boiler based hot water system. Maybe I've picked it up wrongly. I have to HW cylinders each with two immersion heaters running on economy seven plus a boost function via the Horstmann boxes. This is a holiday home so when we leave we leave clocks running but can switch off the feed on the box to the two heaters spurs. I'd like to be able to remotely switch this back on a day before so that the water heats the night before we arrive. I've just been thinking and maybe the answer is to look at the switching on the fused spur to the main immersion heater and just the leave the box running as normal. That might work? Can I make that fused spur remotely controllable I wonder.
 
It's basically using the hive to control a relay / contactor.

You have 4 elements to control each drawing 13a.

The smart heating controls are rated at less than 5a so the signal from the smart controls is used to operate a contactor rated at >13a for each element.
Otherwise your smart controller would become very hot and very dumb very quickly.

It is relatively easy to do but how it is done depends on how much control you want over the system and how much you want to spend.

One signal can operate as many switches as you like.

Once you explain what it is you want most electricians will be able to make it work for you but it is certainly not a diy project.
 
Hi dave, new to the forum, i try to specialise in automation and smart home is somthing i am currently working on myself.
Your immersion heater will draw to many amps for the low amp controls of nest hive or tasimo.
Wireless controlled switched spur could work but would then be separate to your smart system requiring a different app etc.
You could connect to nest or hive by running the lower amp relay to control some higher powered relays that are separate.
This would mean all your controls would be accessible remotely.

If you would like more info on this. Let me know. Or i can take a look for you as Perth is just down the road.
Mike
 
I've just edited your post @Michael Burns to remove your email address from the public forums.

I know it's your choice to post it, but we generally remove them to try and avoid them being scraped by spammers.

The forums have a private messaging facility, so if you've got it enabled (in your profile) one or the other of you should be able to start a conversation with the other and exchange details in private.

Regards

SC
 
If it’s only to give the hot water a head start why not only connect one element that way you can switch the rest on when you get there, unless you are jumping straight into a bath on arrival I can’t see any point
 
Yes broadly you are right, but for paying guests id like to have the hot water available. Thanks
I've just edited your post @Michael Burns to remove your email address from the public forums.

I know it's your choice to post it, but we generally remove them to try and avoid them being scraped by spammers.

The forums have a private messaging facility, so if you've got it enabled (in your profile) one or the other of you should be able to start a conversation with the other and exchange details in private.

Regards

SC
I've just edited your post @Michael Burns to remove your email address from the public forums.

I know it's your choice to post it, but we generally remove them to try and avoid them being scraped by spammers.

The forums have a private messaging facility, so if you've got it enabled (in your profile) one or the other of you should be able to start a conversation with the other and exchange details in private.

Regards

SC

Cant see how to enable the private messaging, sorry.
 

Reply to evening from Scotland- advice if possible. in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hoping someone maybe able to help. We have a Horstmann electronic 7 that's connected to the water heater element(everything been great for years)...
Replies
2
Views
1K
Hoping someone maybe able to help. We have a Horstmann electronic 7 that's connected to the water heater element(everything been great for years)...
Replies
3
Views
1K
Daughter has bought a house and it has a home security system, G-Tag setup. Issue is the alarm panel displays are pixelated and you cant see...
Replies
0
Views
656
Hi all, I have a slightly mish-mash heating set up, in that downstairs I have wet underfloor heating with an individual thermostat per room, but...
Replies
1
Views
2K
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
Replies
4
Views
627

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock