Discuss everynights a 17th edition night in the Australia area at ElectriciansForums.net
Good. Sometimes, but often you won't find it in the index so you'll need to know which sections are applicablenot more than 2.75m from the ground reg 537.6.3, i find it easier by going to index at back, whats your thoughts
Good. Sometimes, but often you won't find it in the index so you'll need to know which sections are applicable
Minimum CSA for earth conductor on a TT supply............
I found when taking my 17th and indeed doing the revision questions leading up to it that you could generally pick a key word in the question that you then find in the index...........
i know in my head it is 6mm but cant find it in regs.. im @ 542.1.6
feel as if years away of knowing the sections.... index slightly easier, but are they all there... 17th exam in 2 weeks
Table 54.1...........
What is the maximum Zs for a circuit protected by a 30A BS3036 Fuse?
PM me if u want a bunch of test questions..............all PDFs
2.5mm protected against mechanical damage , 16mm if not, isit thumbs up???
It was 2.5mm sq I was looking for......protected against mechanical damage and sheathed
What is the required minimum impulse withstand voltage for a 230V installation of category II equipment?
so does that mean if is 2.5mm it has to be in conduit or trunking ..
Name three electrical sources for safety services?
2.5kv ......
560.6.1isit chapter 56 560.6.9 .10 .11 .12???? page153
Yep three examples of what could be used as a source for safety services (they are listed in that reg).now your getting personal topquark,, it sounds like you asking for a list, and he tells us c&g love lists....
Is it acceptable to use a TNC-S (PME) type earthing system on a caravan site for a permanent building?
Is it acceptable to use a TNC-S (PME) type earthing system for earthing a static caravan (the chassis would need to be earthed for this)?
Yes to the first, no to the second.id say no to both 7.21.411.4... somehting tells me bond the chasis
1.09 ohms tabe 41.2 and which i would multiply by 0.8 to get my max value in the real world
Have a read of section 708 in the new edition. Generally it is thought that PME is not allowed on a caravan site. There is however an exception that allows it to be used for permanent buildings IE offices etc. But it should NEVER be used for feeding either static homes or mobile caravans.
What is the maximum Zs for a circuit protected by a 30A BS3036 Fuse?
What if it is measured at 20 degrees C?
who declares the date for the first inspection and test of an installation following initial verification?
Can you define High Voltage according to the BS (shortened for laughter value)
Actually it's either, alltough I believe the exam wants the answer as the designer.you as the inspectoarte, im shooting off hip here now... i know it says it somewhere...
who declares the date for the first inspection and test of an installation following initial verification?
isit 622..
Actually it's either, alltough I believe the exam wants the answer as the designer.
you were winding me up willder about 20 degrees on zs... bet you scitter when younger,,,,
Reply to everynights a 17th edition night in the Australia area at ElectriciansForums.net