cliffed

-
Arms
Supporter
Reaction score
645
just thoughts on this one.
Existing supply to barns from REC,300 amp Tncs 3p,cabling to House,fused of this via 100 amp cutout,by REC
Sub main 16 mm 2 core,to house.
Will the main bonding conductors be the size of the existing supply ie: 300 Amps regarding the neutral.
 
Is the 'submain' a private cable or DNO? If DNO they may be able to provide a TNCS connection at the load end if you enquire and you could then treat it as a 100a TNCS incomer..
 
Hi - I think it's likely 25mm or 35mm would be needed (from Table 54.8). Not much help if it's all been installed and paved over, sorry ...
 
Thanks,it frustrating,it’s been in forever,I’ve spotted it,but ain’t sure what’s gonna happen,most probably stay like it is
 

Reply to Existing REC & house supply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi there, I was wondering if anyone could advise me on the WT Henley Series 8 house service cutout. I have one of these installed at my house and...
Replies
3
Views
537
Hi I have a customer who has a kiosk with 100 amp cut out fuse supplied from UK power, he needs to bring the power 178 meters to his house, He...
Replies
8
Views
951
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock