Discuss explanation of using 2.5mm2 T+E for a spur from a ring 32A (ring) in the UK Electrical Forum area at ElectriciansForums.net
Thankyou littlespark, then my question is, if we can use 2x2.5mm T+E to create a ring on a 32A breaker. If I add a spur from a junction box or socket outlet, is there a calculation or any evidence in BS7671 to explain why this cable 2.5mm spur isn’t at risk of overheating ? I don’t understand the scientific/ numerical aspect behind this.For an UNFUSED spur there is a limit of only one point. Which, if a double socket, is maximum 26A if both outlets are used with a 13A plug.
Very unlikely that would happen, so we assume a max 20A load on that spur…. And 2.5mm cable can easily take 20A.
We use 32A on a 2.5 ring, because it IS a ring.
Any point is supplied by 2 x 2.5 cables…. Not just one.
433.3.1 (ii) applies in the case of a spur from a ring.Thankyou littlespark, then my question is, if we can use 2x2.5mm T+E to create a ring on a 32A breaker. If I add a spur from a junction box or socket outlet, is there a calculation or any evidence in BS7671 to explain why this cable 2.5mm spur isn’t at risk of overheating ? I don’t understand the scientific/ numerical aspect behind this.
....443.1.204 ....
Reply to explanation of using 2.5mm2 T+E for a spur from a ring 32A (ring) in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.