Discuss Export Limitation in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Reaction score
6
I received a call from a person who was not a customer of mine asking to connect up his 8 kW PV system.

Its a new build and the modules were installed when the scaffolding was up, this was several months ago.

System is 2 x ABB PVI 3.6-TL-OUTD inverters connected to 32 x 250 watt modules. The inverters are installed in the loft area and two twin & earth's have been installed back to the C/U.

The original installation company did not complete a G59 application and I have just done this but SSE have come back and they want ÂŁ20k to upgrade their transformer and then they will allow the full 8kW to be connected. Obviously, my customer is not going to pay ÂŁ20k !

He could just connect up one system but as its a large house with a wedding venue attached to the same supply he would like the full 8kW connected.

There is a system manufactured by Siebert but this needs a data wire installed from the intake to the inverters which as the house is nearly completed would be impossible to install without a lot of damage to the house.

Can anyone think of a way that would limit the total export to 3.69 kW which would keep the DNO happy ? off the top of my head I was thinking of some sort of battery system that one of the inverters could be connected to and then it would discharge via a transfer at night ??

All thoughts appreciated.
 
I think the sibert option can function without the link to the inverters, just by fitting a contactor to cut off one of the 2 inverter circuits if export exceedes 3.68kW
 
Hi,who was responsible for the original survey? ...They weren't by any chance,recently unemployed from an Irish renewable Co. ;)
 
Gavin's correct - our independent electro-mechanical failsafe can simply shut down the inverter if the absolute export threshold is breached. However, if no comms link to the inverters is present then, technically, you are not fully compliant with the ER G100 framework, which requires "granular monitoring data upon request". You would also not avail of the full energy flow monitoring through the facility (generation, consumption, grid-exchange) and also no inverter events/alerts/failures etc would be monitored or reported on. You would also lose the facility of maximising on generation at all times - just leaving a binary on/off scenario for the 2nd inverter.

However, in this particular instance, a simple shut down of one of the two inverters if >3.68kW is exported back to the grid, with an adjustable auto-reset timer, may well be adequate to appease the DNO.
 

Reply to Export Limitation in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'm currently working on a project to upgrade an existing renewable energy system and could really use some expert advice. The...
Replies
0
Views
678
Hello everyone, I currently have two solar modules left over from an installation and I would like to use them to set up a solar system on the...
Replies
3
Views
921
Hi, I'm new here, having recently had nearly 13kWp of solar panels installed on a barn roof, feeding into two Solis inverters (covering about 10...
Replies
25
Views
8K
Hello All Can I say to start with I am not an electrician but used to be a heating engineer (yes I can hear the groans). I have wired the...
Replies
85
Views
14K
I'm in the middle of preparing a quote for installing 12 x 3Kw and 4 x 2Kw halogen heaters in a church. The system design was provided by a...
Replies
27
Views
997

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock