I have a consumer unit to move for my final assessment for NAPIT, the cables are too short. it is currently too tight to the ceiling.

What is recommended to extend the cables by no more than 20 cms.

Thank you Eleanor
 
adaptable din railbox. like here:
 

Attachments

  • dinrail.JPG
    463.5 KB · Views: 76
There's a couple of options, joint in the new CU using Wagos or use a DIN rail enclosure and suitable DIN blocks and extend the cables to where you need them.

Note: Be careful using DIN rail earth blocks as they will tie all the CPCs together in the DIN enclosure rather than the CU so you can get false measurements when doing R1+R2 etc.
 
There's a couple of options, joint in the new CU using Wagos or use a DIN rail enclosure and suitable DIN blocks and extend the cables to where you need them.

Note: Be careful using DIN rail earth blocks as they will tie all the CPCs together in the DIN enclosure rather than the CU so you can get false measurements when doing R1+R2 etc.
First time I used DIn Rail blocks I had this issue and took me a good half hour to realise why my test results were different to what i expected.

Wago make little orange din rail holders for their connectors.
 

Reply to Extend Cables to CU in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hey everyone, working on a new build house and outside garage is wired up like this, however customer wants a Garage Consumer Unit instead of the...
Replies
8
Views
365
Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
795
I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
6K
I am planning to go semi off grid with a victron and battery system. The system will be installed in an out building about 20 meters away from...
Replies
7
Views
804
Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock