Discuss Extending a lighting circuit to s new extension? in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
8
Hi guys n girls,

Building an extension and considering extending the downstairs lighting circuit which is 1.5mm t+e.

It is on a 5 amp breaker and I do not know the current length so am unsure if I can extend to the osg maximum of 105m? Also not sure of the osg maximum for bs3871 type mcb.....

If i measure the resistance at the furthest point of the line conductor and divide by the value for 1.5 (12.10 milli ohms) in table i1 of the osg is this likely to give me an accurate figure for existing length (assuming all connections are perfect).

According to my calcs the highest allowable figure should be 3.17ohms for R1+R2 and 1.27ohms for line on its own.

Am I best just running a new lighting circuit instead on a dedicated breaker? Help or advice appreciated.
 
Off top of my head the Zs for a type 2 5A is between 6 and 6.5 ohm. Does the existing circuit have additional rcd protection.
 
As you are extending the circuit it is now a requirement for all domestic lighting circuits to have additional rcd protection. Are you an electrician.
 
As you are extending the circuit it is now a requirement for all domestic lighting circuits to have additional rcd protection. Are you an electrician.
I new it was a requirement for new installations but wasn't sure if extending an old circuit with an installation done under the old regs whether it would need to comply with the new regs. The electrician question, current level of qualification would be Electrical Trainee but working towards nvq2 and 3.
 
It being a 5A mcb as opposed to 6A suggests that this is quite an old CU so you need to check that a new RCBO will fit correctly and approved by the manufacturer for use in that board.
Ok Dave thanks. Would it be better to replace the cu at this point for an all RCBO unit rather than faffing about with an older unit trying to get new parts to fit etc?
 

Reply to Extending a lighting circuit to s new extension? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’ve got an issue driving me crazy and can’t get anyone to figure it out as it’s not their issue. We had a new extension, single rear...
Replies
9
Views
998
I am looking at installation of an architectural dimmer, that is will supply 6 channels, with 20A circuits each (2400W ea). Our hall has can light...
Replies
2
Views
687
Firstly, please go easy as I'm still a trainee! Working on my L3 2365 I'm having trouble understanding the rationale behind adiabatics...
Replies
3
Views
793
I recently installed a new 15amp circuit breaker, and wired a 14-2 gauge wire to a brand new dimmer switch. From the dimmer switch I daisy chain...
Replies
0
Views
774
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock