Discuss Extending a lighting Circuit in the UK Electrical Forum area at ElectriciansForums.net

G

GEelecs

Hello All,

A friend of mine wants me to put lighting into his attached garage,

He wants 2 fluorescent tube lights (28W) putting in.

I have passed my domestic installer course and 17th edition course last year and I'm Part-P registered.
(I'm currently waiting to register with NAPIT and to be assessed on this circuit hopefully)

I have had a look at his house electrics.

Its a TN-C-S system with the old fuses. (Needs Updating Soon)

I'm sure I can spur off the lights in the living room into the garage but I cant exceed the current rating of the cable.

There are only 4 lights on the circuit each with 60 watt bulbs so 60 x 4 = 240w + 28w (268w)

268/230 = 1.2A.

The lights are wired with 1mm cable. (16A Clipped Direct)

Can I extend a circuit on a old fuse board? I'm sure I can :90:

Cheers

(Advice will be very much appreciated)
 
Last edited by a moderator:
Hello All,

A friend of mine wants me to put lighting into his attached garage,

He wants 2 fluorescent tube lights (28W) putting in.

I have passed my domestic installer course and 17th edition course last year and I'm Part-P registered.
(I'm currently waiting to register with NAPIT and to be assessed on this circuit hopefully)

I have had a look at his house electrics.

Its a TN-C-S system with the old fuses. (Needs Updating Soon)

I'm sure I can spur off the lights in the living room into the garage but I cant exceed the current rating of the cable.

There are only 4 lights on the circuit each with 60 watt bulbs so 60 x 4 = 240w + 28w (268w)

268/230 = 1.2A.

The lights are wired with 1mm cable.

Can I extend a circuit on a old fuse board? I'm sure I can :90:

Cheers

(Advice will be very much appreciated)

you have to make sure the work you complete complies or exceeds the current regulations. Have you checked earthing and bonding arrangements are adequate?
 
I haven't had a look but could I come off the rose?

I had a look around the house there is no bonding to the gas or water but its an old install.
 
GS can you please only post once and not the same post 4 times, each post as to be approved due to you being a new member.
 
Sorry MOD, I wasn't sure how the forum worked, I was wondering where my posts went.

Yes, I will do that first before installing the new lighting circuit, I have noticed that the bonding for the supply seems like 10mm and not 16mm can I change this or do I have to get the board to do this?
 
Sorry MOD, I wasn't sure how the forum worked, I was wondering where my posts went.

Yes, I will do that first before installing the new lighting circuit, I have noticed that the bonding for the supply seems like 10mm and not 16mm can I change this or do I have to get the board to do this?

No Drama it's just that your posts sit in a queue until a member of staff gets to them it's not that you're being ignored, Once you get to 6 posts there is no need to approve each one.
 
Sorry MOD, I wasn't sure how the forum worked, I was wondering where my posts went.

Yes, I will do that first before installing the new lighting circuit, I have noticed that the bonding for the supply seems like 10mm and not 16mm can I change this or do I have to get the board to do this?

Bonding for the supply?
 
Thanks, I was going to check this in my 17th Regs.

So if I bond then take the lighting circuit off the rose or use a junction box.

All will be fine?
 
The old wire fuse board had no RCD because I'm extending a circuit is it mandatory to provide RCD?
 
Last edited by a moderator:
Clipped direct ceiling level and into the attached garage lights will be mounted on the joists, so RCD is required.

Can I fit a RCD/RCBO to a old fuse board? (NOPE)
 
Last edited by a moderator:
All is good then :)

1. Bonding
2. Rose Or Junction box to spur
3. No RCD required
4. Test & Inspect
5. Certificate

Did I Pass :)
 
Last edited by a moderator:

Reply to Extending a lighting Circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello all. So I am sure the expertise on this forum will be able to decode this very easily. But it has completely baffled me. I'm in training so...
Replies
14
Views
614
I was at a customers house changing a socket and they asked me a question about their lights. Some of the lights in the house suddenly get...
Replies
4
Views
690
Hi all, I was thinking to add some lights like in the attached image, basically twin batten lights to my attic but i'm not familiar with strip...
Replies
4
Views
729
Strange on this, we are wiring an extension at the moment and I would like to 3 way the (currently 2 way) landing switch to the new bedroom so...
Replies
14
Views
629
Hi guys, Been asked to fit 2 lights and a switch, which in reality turned out to be rewiring a multiple PIR setup to a single switch, adding...
Replies
0
Views
863

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock