I am faced with some very short cables inside a double socket. What is the best way of extending them? I am thinking Wagos would be acceptable as the back box is accessible, but would like to know the industry standard method please. If anyone can also point me to the appropriate regulation too, that would be great.

Thanks
 
Dont know about an 'Industry Standard' as things have progressed from connector blocks to Wago's or similar MF connectors, which are as good as anything.
Seen crimps been used before but not advisable on solid conductors.
As per Derek Section 526 on connections!
 
I was wondering how good they are, now that the Wagos are well-established as reliable.

Alas, maybe they are not something to bother with if you have some Wagos and the space to use them.
 
Funny you should mention those. Had two ring final faults last week, high end to end on the cpcs. Both circuits had been extended using the inline splices, replaced the ones on the cpcs with alternatives and problem solved.

The others were all OK though? Wonder if it was a defective one, or maybe it had has some abuse.
 
The others were all OK though? Wonder if it was a defective one, or maybe it had has some abuse.
I did four on the cpcs, no way of knowing if it was a dodgy one just did the lot but it was two circuits. Never use any of the Ideal brand connectors.
 

Reply to Extending Cable in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'd like to move the existing socket that feeds the boiler down to where I've pencilled in that can be seen on the photo. The socket to the...
Replies
10
Views
852
We have a room in the house that was the kitchen. That has been relocated to a different area, so the old kitchen has been sold off and the room...
Replies
2
Views
631
I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
5K
Hi I am seeking help and best practices to achieve below tasks. I am not across regulations hence will appreciate best approach to achieve below...
Replies
11
Views
3K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
544

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock