Hi all, looking for some advice with regards to extending cables for a consumer unit change. The old board is a mess inside with cables being cut short etc. What's your go to method for extending. When I've only had to extend a couple I've used the Ideal inline splice connectors, but this is gonna need nearly all of them extending. Din rail connectors in an enclosure seems popular. Does anyone have any pics of their work doing this? Thanks in advance!
 
Din rail connectors would be my go-to solution from how you describe your situation. Wago Topjobs have now replaced the older screw down type... but they both get slotted onto a din rail in a box.
With regards to RFC would you put both legs into one connector or one per connector?
 
Note that green/yellow DIN rail connectors connect electrically to the DIN rail, so to avoid future testing problems, only use a green/yellow for one earth wire, and ordinary ones for the rest of the earths.
So,just pick a circuit and use an green/yellow for that then just use a standard one for the rest yeah?
 
here's one i did a few years ago:
 

Attachments

  • dinrail.JPG
    463.5 KB · Views: 153
Maybe have a look at these guys.

Costs a wee bit more than making it up yourself but if you dont have all the connectors i might save buying them in bulk and not using them.
 

Reply to Extending cables for a new board change in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
789
Hi all! I'm not a spark but know enough to be able to install off grid solar etc. I've just purchased a new house and have noticed the consumer...
Replies
30
Views
5K
I had a consumer unit replacement today. It was a bit of a nightmare as most of the cables were too short for the new unit. I extended the ones...
Replies
24
Views
6K
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
775

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock