It's a Schneider RCBO. The CU is an old square D QO board that I can still get new (although ecoensive) parts for.

Every circuit I touch is being upgraded to RCBO from the original MCB's. When I moved in, the only RCD's in the place were on the electric shower and one of 4 socket RFC's.

You shouldn't fit Schneider (or any other non-square D) devices to a square D board without the explicit 'OK' from Square D.

All MCBs/RCBOs vent super heated gas when they trip. The manufacturers design them so that that gas is vented away from any parts it may damage or cause fire to. By mixing manufacturers you are probably venting hot gas where it may cause damage.
 
You shouldn't fit Schneider (or any other non-square D) devices to a square D board without the explicit 'OK' from Square D.

All MCBs/RCBOs vent super heated gas when they trip. The manufacturers design them so that that gas is vented away from any parts it may damage or cause fire to. By mixing manufacturers you are probably venting hot gas where it may cause damage.
my arse vents super heated gas. should i be worried about non square ARSED BREAKERS?
 
Thanks for the replies all - I've been offline for a while.@dksanders - I called square D (who are now part of Schneider) who confirmed it's ok to fit the device I fitted. In addition, there are several others fitted by the previous owner and passed by the electrician doing the EICR before I moved in. (He did mention that he hadn't physically checked all the cable runs, however, as expected, since some of them are inside walls).
No signs of any overheat or other damage, it's just a total mess. Literally the cables are just thrown into the loft space under the thermal insulation. I just didn't want a possible insurance claim denied in the event of a fire simply because the cables aren't clipped.
 

Reply to Extending wiring - how should I secure the existing untidy wiring? in the DIY Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi, I would like to add a new socket in the bedroom. Current room configuration: 3 existing sockets - wiring coming from the bottom (under the...
Replies
1
Views
689
Hi My 4 bed 2 storey house was extended 2 years ago and completely re-wired, but I am having to upgrade the insulation and board out the loft...
Replies
0
Views
1K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Reaching out for some help/guidance and sanity check. Apologies in advance for the long post, but wanted to make sure it was clear. Thanks in...
Replies
0
Views
959
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
982

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock