I think the 1667 is stupid, it's like someone saying phew at least the RCD will work quick lets go..........It's like going back to previous versions of the regs 15th if memory serves me correctly and using the "alternative method" 50v rule ............personally I would feel much happier if everyone aimed at as low ra as they can, much lower than 200. I for one would be aiming at well below 10 ohms at the very least. If the DNO could only give us 10 ohms on TN supplies there would be an outcry, we'd all have to fit RCD's at every installation's origin. I've worked on many large sites over the years and the engineer on site would never except a ra of 200 let alone 1667 they would always be aiming way lower than 100. 5 - 10 would be accepted after some hard graft but as has been said it's possible to achieve below an ohm in a lot of cases with a bit of hard work with some decent rods. Lower the better IMO
I dont disagree up to a point and I think you will find Skelton doesnt either.
The issue constantly raised by us is that many who scoff at the Bs7671 max values appear to be happy with values which will still not operate an OCPD in a reasonable time, if at all.They are still reliant on an RCD.
Given that a value of 10 ohms or 200 ohms......or even 1667 ohms will make no difference to RCD trip times why aim for a lower value unless you get TN values?