Hi,

I'm updating our bathroom and I'm changing our extractor fan from a simple ceiling mounted one to a more powerful inline version (Blauberg) mounted in the loft.

The fan only had 2 wires - a black and a red.
It has an isolator switch outside the door in a twin switch plate shared with the lighting. (so 2 switches - the left for the fan and the right for the lights).
There is no timer on the current fan.

We are happy for the new fan to run in the same way - i.e. when the switch is on

The new fan however has 3 connections - Neutral (N), Live (L), Switched Live (LT).

I wired up as:
black to N (from the isolator switch this comes from a blue wire)
red to L (again its red to red in the isolator switch).

The fan doesn't work.

I attached photos of the twin switchplate with the isolator switch (on the left) and the top of the fan.
  • You see that the red and black cables I mentioned are 2 core
  • There is then a 3 core + earth running up from the same switch plate to the lighting to the ceiling rose which is now in the loft and accessible.

Can anyone help?


Many thanks,

Chris
 

Attachments

  • 1.jpg
    453.4 KB · Views: 24
  • 2.jpg
    254.5 KB · Views: 23
  • 3.jpg
    225 KB · Views: 22
Last edited by a moderator:
We can only guess here what is the feed to the switch, so someone with a voltage tester would have to clarify….

the 3 terminals in the fan are neutral…. Permanent live, which actually runs the fan and a switched live, this is normally joined to the light so the fan operates when the light goes on, and the permanent live runs on after the light is turned off.
It appears you have a live, switched live and neutral at this switch.
you may also have the same at the light….
 
Hi,

I'm updating our bathroom and I'm changing our extractor fan from a simple ceiling mounted one to a more powerful inline version (Blauberg) mounted in the loft.

The fan only had 2 wires - a black and a red.
It has an isolator switch outside the door in a twin switch plate shared with the lighting. (so 2 switches - the left for the fan and the right for the lights).
There is no timer on the current fan.

We are happy for the new fan to run in the same way - i.e. when the switch is on

The new fan however has 3 connections - Neutral (N), Live (L), Switched Live (LT).

I wired up as:
black to N (from the isolator switch this comes from a blue wire)
red to L (again its red to red in the isolator switch).

The fan doesn't work.

I attached photos of the twin switchplate with the isolator switch (on the left) and the top of the fan.
  • You see that the red and black cables I mentioned are 2 core
  • There is then a 3 core + earth running up from the same switch plate to the lighting to the ceiling rose which is now in the loft and accessible.

Can anyone help?


Many thanks,

Chris
If you put a wire link between switched live and live on the fan,it will work as before.
Regards,S
 

Reply to Extractor Fan (red and black wires only) in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
693
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Replies
14
Views
977
Hi, have an old bathroom fan. Which has two wires the black and red (line and neutral). The fan has no isolator switch and was powered when the...
Replies
3
Views
699
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
409
Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock