bathroom man going to fit extractor fan with timer to a pull switch that only turns on power for shower no light just double checking it is ok to wire into this switch
 

Attachments

  • 20210416_172501.jpg
    258.8 KB · Views: 19
  • 20210416_172537.jpg
    278.5 KB · Views: 18
This is a very bad idea and totally non compliant with the regulations. An electric shower circuit should serve the shower only and nothing else. And there are many other reasons not to do it. Tell your bathroom fitter he's breaking the law by messing with bathroom electrics if he isn't suitably qualified and Part P registered. I hope all this doesn't sound too blunt but these 'jack of all trades' bathroom and/or kitchen fitters can be notoriously bad with electrics !
 
This is a very bad idea and totally non compliant with the regulations. An electric shower circuit should serve the shower only and nothing else. And there are many other reasons not to do it. Tell your bathroom fitter he's breaking the law by messing with bathroom electrics if he isn't suitably qualified and Part P registered. I hope all this doesn't sound too blunt but these 'jack of all trades' bathroom and/or kitchen fitters can be notoriously bad with electrics !
would i be right in saying i would like it wired to ceiling rose so it turns on with the light instead so if i use the bath and not shower it turns on thanks
 
That's right , but there should also be a maintenance isolator for the fan and the manufacturers instructions might also require a 3 amp fuse in line. Also a ceiling rose in a bathroom will often be non compliant now. I strongly recommend you find a decent electrician to help with this side of the work.
 
Blink and you miss it, there is a note at the beginning that states you must be competent and the work must be notified to building control.

strange, in the whole video I never saw any testing or certification so I am not sure how he has notified it.
 

Reply to extractor fan in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Thinking a 240V AC relay activated by two independent light switches could be used to switch power to a shared inline extractor fan. The fan...
Replies
31
Views
2K
Hello, I'm swapping my extractor fan in the UK and I have bought a Turkish extractor fan stupidly and the connections you can see in the picture...
Replies
1
Views
440
Hi, I'm looking to install a new bathroom extractor fan in my bathroom as I have a windowless bathroom and the current one I have installed in...
Replies
13
Views
773
1964 house old style wiring Need to wire a extractor fan up Is it possible to wire the extractor fan to report switch there's 2 red wires in the...
Replies
14
Views
992
Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
808

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock