Ripped form an NIC newsletter.....


The NICEIC are now quoting a figure of 7000ohm (based on 30mA fault current for a disconnection time of 0.4s). It was dicussed in a recent connections magazine and also discussed at one of their tech talks.

From pg 47 in the magazine issue 172
The metallic part can be assumed not to be an extraneous-conductive-part if the following condition is met:
Rcp> (Uo/Ib) - Ztl
where,
Rcp is the resistance between the conductive part and the MET in ohms
Uo is the nominal voltage to Earth in volts
Ib is the value of current through the body in amperes that should not be exceeded. (The value may be taken as 30 mA for a disconnection time of up to 0.4 s, as given in DD IEC/TS 60479)
Ztl is the impedance of the human body in ohms. The value suggested in DD IEC/TS 60479 is 1000 ohms where Uo is 230 V (50 Hz) under dry or wet conditions.
Taking Ib as 30 mA and Ztl as 1000 ohms (as suggested above where the disconnection times in the installation are 0.4 s or less and Uo is 230 V), the limiting value of Rcp is given by:

Rcp > (230/0.03) - 1000
Rcp > 6667ohms


Thus, if Rcp exceeds 6, 667 ohms, the pipe may be considered not to be an extraneous-conductive-part, such that main bonding of the pipe is not required
 
Interesting point Ian, but i think the NIC would have responsibility if anything did happen, especially as they have published it.
 
Hi,

GN8 gives guidance on this using what they term the 'let-go' threshold, quoted as 10 mA.

Using the same equation this gives a value of 22 kohms for the threshold - above this, you would not consider the metalwork extraneous.

It is really a design issue and up to the designer which value of current he doesn't want to exceed (e.g. 10 mA).

Where the NIC get off declaring something like this as fact, I don't know.

I'm sure they help create half of the misunderstanding of the regs that exists.:D

GN8 goes on to say...."the designer would need to consider possible variations in resistance and whether a lower limit on the current flowing through the human body or livestock is necessary"

With this in mind, I think I would be tempted to err on the side of caution and use a lower figure for my current - i.e. 10 - 15 mA, and go for a higher threshold.
Anything lower than the threshold obviously should be bonded.:)
 
thought an ir test between earth and unknown part had to be less than 20k ohms to be considered extraneous, although i cant find a reference to it now
 
so the nice ppl are thinking 6. 6k, and intelligent life thinks 20-23k. i know which figure i will be using!
 
thought an ir test between earth and unknown part had to be less than 20k ohms to be considered extraneous, although i cant find a reference to it now

I seem to remember being told by NIC that a value over 0.25 megaohms would mean that the unknown part would not be an extraneous conductive part.
 
They will have to bring out a guidance book fairly soon with the way they are going and the numerous NIc regs

Its just been on the news
The Niceic has staged a coup d"etat at the IEE building in London
The present IEE administration has been given a visual condition report and found to be out of touch with insanity and electrocuted with an extraeneous plastic pipe
Tony Cable,the spokespark for the Niceic said all rebellious other tribes will now be crushed in the next few weeks

Always knew they had a need to be the dictator
 
OK guys perhaps I wasn't totally clear in my post.
The post I was replying to was talking insulation resistance (ir) test between the MET and unknown part hence the value of 0.25 megaohms.
Hope that's now as clear as mud.
Like the news flash Des.
 
hello everyone, im new to the forum and this is my first post.... just been reading this thread and have a little thing to add....

Surely if the metal pipe has a high resistance to earth it would not be a bad idea to bond it as it would be sitting at around 230v under fault conditions?

or am i just stupid? haha.....
 
Thats the reason for the test is my understanding or we would be bonding everything.

So if the test show that is is not extraneous over 22k then no need to bond.

Hope that makes sence.
 
DETERMINING IF A PART IS EXTRANEOUS OR JUST A PIECE OF METAL
A test should be made using an Insulation Resistance Tester set on MΩ, supplying 500 Volts.
Test procedure:
Connect one test lead to the metal part and the other lead to a known earth. (MET)

If the resistance value is 0.022MΩ (22000Ω) or greater, no supplementary bonding conductor is required.
If it is less than 0.022MΩ, supplementary bonding should be carried out.

From the Ohm’s law:

I = V / R;

I = 500V / 22000Ω = 0.023Amp

This shows that if the fault was on a single phase 230Volt supply the current that would flow between the conductive parts would of course be only 0.0115Amp (11.5 mA).

This current is unlikely to give a fatal shock.

Guidance Notes GN8 and GN5 state:
" If extraneous metalwork is above 22KΩ then it need not be supplementary bonded.

 
hello everyone, im new to the forum and this is my first post.... just been reading this thread and have a little thing to add....

Surely if the metal pipe has a high resistance to earth it would not be a bad idea to bond it as it would be sitting at around 230v under fault conditions?

or am i just stupid? haha.....

This is the problem when the reasons for bonding are not understood, during a fault, the voltage on the main earth terminal rises (sometimes significantly) this can then be distributed to bonded non extraneous conductive parts, creating a danger!

That is why it's important to actually establish whether an item is actually an extraneous-conductive part before we string green&yellow everywhere.
 
gotcha.... if said pipe had a low resistance to earth and its bonded (extraneous) the dis. time would be faster (less danger), if not bonded and theres an earth fault anywhere on the property would just result in another live part to grab with no path to earth (thus no point in bonding it) ... i did know this.... living in Barcelona at the mo, of the tools, the brain is a bit slow at the mo.... i remember that equation regarding a touch voltage not exceeding 50v.... coming back now... thanks mr IQ!

Dave
 
Here's a question for you all regarding this thread..... My poor first post got me doing a little thinking (yes im sad like that, but i am drinking a beer whilst posting)

During a periodic test and inspection of the installation in a butcher’s shop, it is revealed
that the circuit supplying an electrically operated compressor does not meet the maximum
earth fault loop impedance requirements. The circuit is protected by a 16 A
Type C CB, and the unit is situated 1 m from a steel sink. Explain how, under certain
conditions, this situation may be resolved by the use of supplementary bonding.
Support your answer with calculation.

This is not my work, its Brian Scaddan's the 2391 chief examiner.

lets get the old grey old matter going

ill post the answer later..........
 

Reply to Extraneous....Yes or No.... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Recieved my copy of NICEIC/Elecsa 'Connections' magazine and notice they are using a different calculation in determining if a metal part is...
Replies
11
Views
3K
B
Q21 list three things to check when inspecting overcurrent devices A21 (i) correct BS and type (ii) Correct current setting (iii) adequate...
Replies
3
Views
3K
P
Here is a sample paper for the 2382-20 (the update to 17th) answers to follow, enjoy!!! Sample 2382-20 (update for 17th 30 questions) Answers...
Replies
13
Views
29K
maddfridge
M

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock