Ripped form an NIC newsletter.....
The NICEIC are now quoting a figure of 7000ohm (based on 30mA fault current for a disconnection time of 0.4s). It was dicussed in a recent connections magazine and also discussed at one of their tech talks.
From pg 47 in the magazine issue 172
From pg 47 in the magazine issue 172
The metallic part can be assumed not to be an extraneous-conductive-part if the following condition is met:
Rcp> (Uo/Ib) - Ztl
where,
Rcp is the resistance between the conductive part and the MET in ohms
Uo is the nominal voltage to Earth in volts
Ib is the value of current through the body in amperes that should not be exceeded. (The value may be taken as 30 mA for a disconnection time of up to 0.4 s, as given in DD IEC/TS 60479)
Ztl is the impedance of the human body in ohms. The value suggested in DD IEC/TS 60479 is 1000 ohms where Uo is 230 V (50 Hz) under dry or wet conditions.
Taking Ib as 30 mA and Ztl as 1000 ohms (as suggested above where the disconnection times in the installation are 0.4 s or less and Uo is 230 V), the limiting value of Rcp is given by:
Rcp > (230/0.03) - 1000
Rcp > 6667ohms
Thus, if Rcp exceeds 6, 667 ohms, the pipe may be considered not to be an extraneous-conductive-part, such that main bonding of the pipe is not required
Rcp> (Uo/Ib) - Ztl
where,
Rcp is the resistance between the conductive part and the MET in ohms
Uo is the nominal voltage to Earth in volts
Ib is the value of current through the body in amperes that should not be exceeded. (The value may be taken as 30 mA for a disconnection time of up to 0.4 s, as given in DD IEC/TS 60479)
Ztl is the impedance of the human body in ohms. The value suggested in DD IEC/TS 60479 is 1000 ohms where Uo is 230 V (50 Hz) under dry or wet conditions.
Taking Ib as 30 mA and Ztl as 1000 ohms (as suggested above where the disconnection times in the installation are 0.4 s or less and Uo is 230 V), the limiting value of Rcp is given by:
Rcp > (230/0.03) - 1000
Rcp > 6667ohms
Thus, if Rcp exceeds 6, 667 ohms, the pipe may be considered not to be an extraneous-conductive-part, such that main bonding of the pipe is not required