I manage to speak to him today ( he was booked by the lettings agent so not had any contact with him before ) . He said the reason for putting the isolator switch outside and making it waterproof ( even though it was outside zone 2 ) was that if someone was drunk and stepped out of the shower or reached around the bath and switched on the switch ( this is above the door so not easy to reach from either place except if you stepped out) then it would be a safety issue whereas if you went outside the bathroom you were more likely to be dressed .
That is a ridiculous reason if they are not in zone 2 there is no issue.
 
I manage to speak to him today ( he was booked by the lettings agent so not had any contact with him before ) . He said the reason for putting the isolator switch outside and making it waterproof ( even though it was outside zone 2 ) was that if someone was drunk and stepped out of the shower or reached around the bath and switched on the switch ( this is above the door so not easy to reach from either place except if you stepped out) then it would be a safety issue whereas if you went outside the bathroom you were more likely to be dressed .
Complain to Napit. Take some photo's, say you are willing to email them photos and the report, and quote this response.
You can't C2 something in case someone is drunk. It doesn't make sense anyway, by his logic you would need IP rated switches in the kitchen in case you washed up and then turned something on.
 
he mentioned that the lights are IP20 . So if they are outside zone 2 , they should still be ok ?
Outside of Zone 2 i.e. just like anywhere else in the property IP2x is acceptable to the regs.

Would I fit them, depends, good modern ventilated bathroom, probably, old unventilated bathroom I would more than likely fit a higher rated fitting, however this would be by choice not compulsory.
 
Outside of Zone 2 i.e. just like anywhere else in the property IP2x is acceptable to the regs.

Would I fit them, depends, good modern ventilated bathroom, probably, old unventilated bathroom I would more than likely fit a higher rated fitting, however this would be by choice not compulsory.
thank you for the advice
 
Complain to Napit. Take some photo's, say you are willing to email them photos and the report, and quote this response.
You can't C2 something in case someone is drunk. It doesn't make sense anyway, by his logic you would need IP rated switches in the kitchen in case you washed up and then turned something on.
sorry can I also ask...the socket under the kitchen sink he will not pass the report if it is not waterproof when I asked what regulation it is voilatiing as he said it is a safety hazard ..so i am a bit stuck there . I cant remember if there is a second switch but he mentioned 2 and changing them both. Since there are to plug in a dryer /washing machine ( there is no space in the kitchen for this and I am having the cracked plug in the garage replaced where the dryer and washing machine machine are plugged in , I was thinking of getting this taken out once I make sure it is not in use .

But if it is and if there is no regulation do i still have to change it ? and can he refuse to give me a pass eicr just for this issue . But if it really is a safety hazard I can look at changing ot taking this outswitch under sink.jpg
 
and can he refuse to give me a pass eicr just for this issue
One of the flaws of the system is that the inspector has the final say.
But the inspector is supposed to test according to the regs. There is also a document called Best Practise Guide 4 (free online).
The scheme he belongs to (the same scheme as I do) has rules. The scheme rules are that complaints must first be made in writing to the electrician concerned. If that doesn't get anywhere, then you can complain to Napit.

I would draft a letter of complaint, saying other electricians (including other Napit members) do not agree with the observations, and could they help get this matter resolved. See what happens.
 
One of the flaws of the system is that the inspector has the final say.
But the inspector is supposed to test according to the regs. There is also a document called Best Practise Guide 4 (free online).
The scheme he belongs to (the same scheme as I do) has rules. The scheme rules are that complaints must first be made in writing to the electrician concerned. If that doesn't get anywhere, then you can complain to Napit.

I would draft a letter of complaint, saying other electricians (including other Napit members) do not agree with the observations, and could they help get this matter resolved. See what happens.
ok thank you..that is really good advice
 
There is nothing wrong with that socket. Please tell me this isn't the same electrician you are using to replace your consumer unit in the other thread.
yes he did the original EICR but I am getting another quote as well. Both have said parts are unavailable/expensive to source and best to replace . He is adamant on not issuing the pass certificate if I do not get this changed . He kept saying it is your house and you can do whatever you want but this has been listed as a C2
 
Being generous, this is just another case of an electrician testing to what he thinks the rules should be, not what they actually are.
Being not so generous, it could be viewed as a money generating exercise.
Condemning the socket under the sink (on IP grounds) is beyond ridiculous. It's even mounted on the structure of the house, rather than the cupboard carcase (for which there is a tenuous argument that it's not permitted.)
Regarding the bathroom lights, there is a regulation that requires equipment to be suitable for the environment into which it is installed, but unless there is evidence of considerable condensation in this bathroom, I wouldn't consider this remotely applicable.
If fitting new lights in a bathroom, I think most of us would fit IP rated ones, but they are not a requirement.
 
Being generous, this is just another case of an electrician testing to what he thinks the rules should be, not what they actually are.
Being not so generous, it could be viewed as a money generating exercise.
Condemning the socket under the sink (on IP grounds) is beyond ridiculous. It's even mounted on the structure of the house, rather than the cupboard carcase (for which there is a tenuous argument that it's not permitted.)
Regarding the bathroom lights, there is a regulation that requires equipment to be suitable for the environment into which it is installed, but unless there is evidence of considerable condensation in this bathroom, I wouldn't consider this remotely applicable.
If fitting new lights in a bathroom, I think most of us would fit IP rated ones, but they are not a requirement.
ok thank you Brian...this is the first time I am renting a place so i guess there is a lot to learn :)
 
yes switch was not cracked before inspection but i will have it replaced for sure
Hang on..... so, the inspecting 'electrician' damaged the faceplate?!
 
Hang on..... so, the inspecting 'electrician' damaged the faceplate?!
yes it was not cracked before . My dryer was plugged into it before and I used it regularly and there was no crack .

We were not in the property when the EICR was done as the lettings agent arranged it . I have asked if the plate was damaged when the testing was done but not had a response .
 
Going back to the original report, I would be very interested to know how quickly the RCD trips when you press the test button.
The readings on the report say >500 (x1) and >410 (x5). Assuming these are milliseconds, I think that even without a testing machine you could discern if it trips in 'about half a second' or 'instantaneously'.
If it proves that the RCD is in fact ok, then as far as I can see we are now reduced to one incorrect breaker and a possible shower circuit issue.

General point -
When I (rarely) do remedial work for someone else's EICR, if I disagree with a C2 I justify why on my write up citing relevant regulations and photographic evidence why . You don't actually need a certificate that says "satisfactory", you need written proof that required remedial work has happened, and for me I just use a letter. Here's two excepts from a recent one I wrote:

1642004898949.png

and a bit later:
1642004968350.png

My point is that you don't need the same person to do remedials, and you don't need another EICR, you just need someone to evaluate matters and do required remedials who takes a professional approach.
All the best with this.
 
Back at #55 there was mention of a cracked socket for washing machine and dryer?

It’s likely to crack again with two high load appliances being used at the same time.

Just an observation.
If a 2G socket has been provided for a washing machine and an adjacent tumble drier, then it should be replaced by a dual box and 2 x 1G sockets. (As it should have been on first installation)
 
My point is that you don't need the same person to do remedials, and you don't need another EICR, you just need someone to evaluate matters and do required remedials who takes a professional approach.
All the best with this.
More to the point, you need someone, like timhoward, to do the first EICR. Someone who knows what he's doing.
 
Last edited:
Being generous, this is just another case of an electrician testing to what he thinks the rules should be, not what they actually are.
Being not so generous, it could be viewed as a money generating exercise.
Condemning the socket under the sink (on IP grounds) is beyond ridiculous. It's even mounted on the structure of the house, rather than the cupboard carcase (for which there is a tenuous argument that it's not permitted.)
Regarding the bathroom lights, there is a regulation that requires equipment to be suitable for the environment into which it is installed, but unless there is evidence of considerable condensation in this bathroom, I wouldn't consider this remotely applicable.
If fitting new lights in a bathroom, I think most of us would fit IP rated ones, but they are not a requirement.
I think you are being generous assuming it was actually a properly qualified electrician doing the EICR
 
If a 2G socket has been provided for a washing machine and an adjacent tumble drier, then it should be replaced by a dual box and 2 x 1G sockets. (As it should have been on first installation)
I need to check whats plugged in ...could
Going back to the original report, I would be very interested to know how quickly the RCD trips when you press the test button.
The readings on the report say >500 (x1) and >410 (x5). Assuming these are milliseconds, I think that even without a testing machine you could discern if it trips in 'about half a second' or 'instantaneously'.
If it proves that the RCD is in fact ok, then as far as I can see we are now reduced to one incorrect breaker and a possible shower circuit issue.

General point -
When I (rarely) do remedial work for someone else's EICR, if I disagree with a C2 I justify why on my write up citing relevant regulations and photographic evidence why . You don't actually need a certificate that says "satisfactory", you need written proof that required remedial work has happened, and for me I just use a letter. Here's two excepts from a recent one I wrote:

View attachment 93954

and a bit later:
View attachment 93955

My point is that you don't need the same person to do remedials, and you don't need another EICR, you just need someone to evaluate matters and do required remedials who takes a professional approach.
All the best with this.
Also does the person who does the remedial work charge to.issue the EICR certificate . Or do I go back to te original EICR engineer to.show him the work done report . The guy who.has quoted me.for remedial.work is also charging me for a EICR certificate . Not sure how this works
 
Also does the person who does the remedial work charge to.issue the EICR certificate . Or do I go back to te original EICR engineer to.show him the work done report . The guy who.has quoted me.for remedial.work is also charging me for a EICR certificate . Not sure how this works
I slightly despair at the system sometimes....it's not obvious how it is supposed to work.
The thing is, people like to end up with a certificate that says "Satisfactory". Like a car MOT. But the PRS law clearly says you just need written evidence that the remedial work has been done (I quoted the law in the letter I previously posted).
So you might reasonably be charged for some admin time to write a letter, but it isn't necessary to have another EICR report / certificate done. That said, if the fee is modest there is nothing wrong with having another set of EICR paperwork with no (or only C3) observations, and Satisfactory on the front.
Hope that helps.
 
I slightly despair at the system sometimes....it's not obvious how it is supposed to work.
The thing is, people like to end up with a certificate that says "Satisfactory". Like a car MOT. But the PRS law clearly says you just need written evidence that the remedial work has been done (I quoted the law in the letter I previously posted).
So you might reasonably be charged for some admin time to write a letter, but it isn't necessary to have another EICR report / certificate done. That said, if the fee is modest there is nothing wrong with having another set of EICR paperwork with no (or only C3) observations, and Satisfactory on the front.
Hope that helps.
Hi Tim

He will charge £120 to.issue a pass/ new EICR . Can i submit the oŕiginal EICR with the evidence or remedial work done . And who do I submit this to.please
 
sorry can I also ask...the socket under the kitchen sink he will not pass the report if it is not waterproof when I asked what regulation it is voilatiing as he said it is a safety hazard ..so i am a bit stuck there . I cant remember if there is a second switch but he mentioned 2 and changing them both. Since there are to plug in a dryer /washing machine ( there is no space in the kitchen for this and I am having the cracked plug in the garage replaced where the dryer and washing machine machine are plugged in , I was thinking of getting this taken out once I make sure it is not in use .

But if it is and if there is no regulation do i still have to change it ? and can he refuse to give me a pass eicr just for this issue . But if it really is a safety hazard I can look at changing ot taking this outView attachment 93928
Also just to add in the bathroom anything under the bath/shower basin is considered to be zone 1, however if a tool is required to access under the bath/shower then it doesn’t have any zone.
 
Hi Tim

He will charge £120 to.issue a pass/ new EICR . Can i submit the oŕiginal EICR with the evidence or remedial work done . And who do I submit this to.please
Yes you can but please do not use the same electrician find someone reputable. Some of these apparent Code 2s a different electrician will say works are not required.
 
Hi Tim

He will charge £120 to.issue a pass/ new EICR . Can i submit the oŕiginal EICR with the evidence or remedial work done . And who do I submit this to.please

you cannot pay for a pass. So charging £120 for a EICR with a pass is not possible.

you’ve already paid for the EICR. It Came back unsatisfactory. That’s it, no new EICR is required. Just proof the issues it came back unsatisfactory for have been rectified.

i normally issue a statement of fact listing works I have done.

if I strongly disagree with a coding that has resulted in a fail, I will state this that no works where required due to my belief the installation does not require it to acheive a satisfactory ( only ever done this once).

at the bottom of the statement of fact I would write-

i have carried out all works to bring (installation address) up to a standard to achieve a satisfactory based on EICR cert number 123456 done on (date done) by (contractor business name).
 

Reply to failed EICR, please can you advice in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Private tenant since 2011. First ever eicr February 23 informed via text it failed by text from electric secretary arranging appointment for...
Replies
12
Views
600
Hi, I have a property that I was looking to rent out. Its 12 years old property so relatively new. I had a EICR done from a qualified electrican...
Replies
59
Views
7K
Hi all Called to do an EICR on a property 4 studio flats / bedsits within a single house. The t&e sub main to each flat runs within the fabric of...
Replies
4
Views
2K
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock