Yo folks,

Not sure that this isn't the second post on same topic, first hasn't appeared. Apologies if so.

Ahead of altering upstairs lighting circuit to add a couple of downlights to an ensuite I carried out the usual tests. Got odd IR results. L-N >1000, L-E >1000, N-E 10!. Did a bit of poking around in the loft and found a spider wired downlight arrangement for main bathroom downlights. JB plus wagos. Removed the arrangement and the IR leapt to >1000. Tested each leg of spider, >1000. As I added eah leg of spider the IR fell away to 10 again. This will be fundamental but it eludes me at present. Any ideas, solutions. Is this typical of spider wired downlights? I tend to daisy chain my own installs.

yours,

Rob
 
It could also be damaged cable that is only showing up on the IR test when in a certain position.

Tis odd. The jb is a tad cramped. The IR reading tumbles each time I add another leg of the spider. I'll end up rewiring in a daisy chain and test it again. See what gives.
 
So all cable dissed fro CU ?
Yes. When connected to CU, the initial readings were L-N >1000 Mohms, L-E >1000, N-E 7.62. Disconnected the readings were the same for L-N, L-E but had imprived slightly on N-E to 10 Mohms. I realise thats a 'pass' but curiosity got the better of me. The property was rewired 4 years ago with the downlights added shortly afterwards during a bathroom refurb. Theres a cert for the rewire but not for the alteration.
 
Yes. When connected to CU, the initial readings were L-N >1000 Mohms, L-E >1000, N-E 7.62. Disconnected the readings were the same for L-N, L-E but had imprived slightly on N-E to 10 Mohms. I realise thats a 'pass' but curiosity got the better of me. The property was rewired 4 years ago with the downlights added shortly afterwards during a bathroom refurb. Theres a cert for the rewire but not for the alteration.

I can only surmise that when the JB is reconnected ( thats the reason I asked if you tested with the cables not pushed into the JB ) there is, maybe some damp or something, a strange one that isn't it sorry can't be of any help other than my suggestions.
 
I can only surmise that when the JB is reconnected ( thats the reason I asked if you tested with the cables not pushed into the JB ) there is, maybe some damp or something, a strange one that isn't it sorry can't be of any help other than my suggestions.
Cheers Pete, your interest is appreciated. There's some slack in the cables at the jb, I'll remake connections after a visual inspection. I'll let you know if I suss it. Rob.
 

Reply to Falling insulation resistance in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Replies
4
Views
1K
Downstairs lighting is tripping rcd. Circuit has 4 chandeliers with multiple bulbs and led downlights in the bathroom. Can I just test IR on...
Replies
3
Views
1K
Just done my exam, passed everything except Insulation Resistance... I can't think how I could've failed because it isn't the hardest thing on...
Replies
3
Views
2K
What are the dangers of poor insulation resistance results (i.e <1Mohm) between neutral and earth? If all other tests are ok, what are the...
Replies
8
Views
5K
Evening all, as I’m preparing for my Inspection and Testing exam, I wonder if you might put me straight on something please? When performing a...
Replies
1
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock